Hi all,

My electrical shower suddenly stopped working. I thought it was broken and then bought a new one. But the new shower still does not work. So I tested the cable, found only 55 volts in the electrical shower between live and neutral. But on DB, it is 240 between live and neutral.

It is really strange that it is just a short cable buried in the wall,how come voltage drop is so big? also in the last 2 years the shower worked quite well, anyone has any ideas?

thanks a lot for any help.
 
just checked the isolator, dam, the cable has melted there, i have to replace the isolator,

the shower is 8.5kw, cable is 6mm2, this should be fine, also i have used it for 2 years, but it only melted recently?
 
just checked the isolator, dam, the cable has melted there, i have to replace the isolator,

the shower is 8.5kw, cable is 6mm2, this should be fine, also i have used it for 2 years, but it only melted recently?

Are sure about the 6mm and i'd be inclined to replace the isolator
 
Last edited by a moderator:
do you mean 6mm is not enough?
if its a decent length of run and has insulation round it your on the limit with a 8.5kw shower
not ideal.
had plumber a ring me up today asking about a shower swap a customer had bought .
"can i put this 10.5kw instead of the broken 8.5kw which is on 15m run of 6.0mm2"
answers on a post card
 
it has to be a loose connection
if shower cable check the board and then check the switch
failing that check shower
if none of that
you need a complete rewire
and a new substation
what a bummer
I can give you a price on all
 
what size breaker you got on that 6mm cable there?

correct me if i'm wrong - rough current demand of the shower

8500/230 = 36.95

CCC of cable is dependant on installation method but you'd probably be looking at most ~34A
 
Last edited by a moderator:
what size breaker you got on that 6mm cable there?

correct me if i'm wrong - rough current demand of the shower

8500/230 = 36.95

CCC of cable is dependant on installation method but you'd probably be looking at most ~34A


it is 40A, looks all right
 

Reply to Help: very low voltage in shower! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
2
Replies
20
Views
1K
  • Question
As above, check the whole cable run and look for damage or any junction boxes that might have trouble inside them. Water getting in is a common...
Replies
2
Views
902

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top