Help with some questions
stekel
Hi everyone can anyone help me with some questions im stuck on please
1. Find the CSA of a single copper cable 500m long, which carries a current of 2.5 amperes and has a volt drop of 3.58 volts. Take the resistivity of copper to be 1.72 x 10[SUP]-8[/SUP] ohm/metre[SUP]3[/SUP].
1. An immersion heater takes a current of 13A and is fed through a twin cable, each core having a CSA of 2.5mm[SUP]2[/SUP]. If the conductors are made of copper and have a resistivity of 1.72 x 10[SUP]-8[/SUP] Ω/m[SUP]3[/SUP], calculate the greatest length of cable which may be used, if the cable voltage drop is not to exceed 11.5 volts.
1. A motor takes 45A from a 230v supply. A twin aluminium cable 40m in length feeds the motor, each core having a CSA of 16mm[SUP]2[/SUP]. Calculate the voltage at the motor terminals. Take the resistivity of aluminium to be 2.65 x 10[SUP]-8[/SUP] ohm/metre[SUP]3[/SUP].
Hi,
Generally, folk learn stuff easier if they have a punt themselves, so what are your initial thoughts?
Saying that, you're not helped by the fact that the units of resistivity (Greek symbol "rho", ρ) is actually Ω.m, not what is stated in your questions. (The value is correct, though.)
Ask yourself: do you know any equations that link resistivity, length, area, and resistance? And if you don't know one of those values, can you get it by using other information you're given in the question, and a really well known equation that all trainees should know?
Have a think, have a crack at it, show us your calculations, then I'm sure we'll be able to help some more. :)
Theres a good book on electrical calculations that you can download from one of the sticky posts.
I'll get back to you with the name as i cant remember it at the moment but it helped me with the resistivity formulas
you have 2 formulae to use here. 1 is in BS7671 and is the formula to use to calculate volt drop ( transpose as necessary), and the other is A =Πr²
Thanks for the help guys. okay ill give them a crack
1. R=V/I=3.58/2.5=1.432Ω A=Πxr²=3.142x1.432²=6.44A
I don't think he needs the second one, Tel? (area of a circle).
stekel, you got the first bit spot on in post #8, you correctly used Ohm's Law to determine the resistance of the 500m cable - good stuff! :)
Now you need to relate resistance ("R") with resistivity ("ρ"), length ("l") and cross sectional area ("A"). You now know 3 of these values, you need to work out the 4th.
Good luck, let us know how you get on :)
Morning steve. Thanks for the imput. question 3 i have tried also my answer is on post 10#. any feedback on that would be great.
Steve
3. R=V/I=230/45=5.1 V=IxR=45x5.1=229.5V
no. you need to calculate R from the resistivity and the cable length. you have the resistivity in ohms/cu,m. this you need to convert to 16mm² for 1m, and then x the length.
Been long time since i did any of these so i am definitely rusty. I get 6.0mm2 for the 1st question. I am not 100% sure if this is correct though to be honest!
i got 10mm for q.1. not 100% confident though, it's been 40 years. nowadays i just use the mV/A/m tables for what i need.