Hi Guy's, Need your take on a commercial office IT environment. I am getting earth leakage total of 26mA, okay, spread over 22 workstations & 4 Server & ups IT devices, not bad. The power RFCircuits are fortunately spread over a split load board / 2 RCD's. No nuisance tripping reported. Subject to 543.7.1.3.203 High integrity earth connections is necessary etc. I have yet to remove a Socket to inspect as I need to shut down their servers on this weekend. I do know that at the DB the circuits are 2.5mm T&E so cpc is undersized. Just to confirm on a EICR how would you code it, & any further comments welcome. Thanks, guys in advance.
 
Hi Guy's, Need your take on a commercial office IT environment. I am getting earth leakage total of 26mA, okay, spread over 22 workstations & 4 Server & ups IT devices, not bad. The power RFCircuits are fortunately spread over a split load board / 2 RCD's. No nuisance tripping reported. Subject to 543.7.1.3.203 High integrity earth connections is necessary etc. I have yet to remove a Socket to inspect as I need to shut down their servers on this weekend. I do know that at the DB the circuits are 2.5mm T&E so cpc is undersized. Just to confirm on a EICR how would you code it, & any further comments welcome. Thanks, guys in advance.
I would code the situation as "needing further investigation" If you feel there is a danger, then time should be arranged for a system power down to enable this "further investigation", the client needs to be made aware of the possible consequences of leaving the installation in it's current state, should there be a problem.
 
If you can confirm the CPC size then FI is not appropriate IMO. I would say a C3 so long as there is no nuisance tripping.
The OP has stated in his opening post that he has a measured Earth Leakage of 26 mA regulation 543.7.2.201 clearly states that Final circuits feeding socket outlets or connection units, where the pcc in normal service is likely to exceed 10mA then they require a high integrity cpc, the cpc of a Radial circuit should be in the form of a ring, and if the circuit is in metallic conduit or metallic trunking an extra cpc should be installed.
Diagrams depicting this can be found in the 18th edition OSG Page 87, the I have to disagree with essex ensuring the size of the cpc is not sufficient in my book.
 
One of the problems here is the OSG and BS7671 contradict themselves.
BS7671 requires there be two CPCs.
The OSG just one CPC, terminated at different terminals at each accessory.
 
From what I can see this leakage is a combined sum over several final circuits thus each final circuit may be less than 10ma.
 
Hi Guy's, Need your take on a commercial office IT environment. I am getting earth leakage total of 26mA, okay, spread over 22 workstations & 4 Server & ups IT devices, not bad. The power RFCircuits are fortunately spread over a split load board / 2 RCD's. No nuisance tripping reported. Subject to 543.7.1.3.203 High integrity earth connections is necessary etc. I have yet to remove a Socket to inspect as I need to shut down their servers on this weekend. I do know that at the DB the circuits are 2.5mm T&E so cpc is undersized. Just to confirm on a EICR how would you code it, & any further comments welcome. Thanks, guys in advance.
Just to clarify something Westeard10 mentioned, can you clarify how many circuits you are talking about, in essence if its more than one circuit what is the max EL measured per circuit, or is it just 1 circuit, in hindsight should have asked these question before I went chapter and verse, good point Westward though.
 
Would it be possible to split the 2 rfc's into 4 radials on their own RCBO thereby removing the need for high integrity earth? If there are no spare ways then a new extra board would be easier than practically rewiring the place.

I suppose it depends on wether the leakage is distributed evenly across the circuits but it may remove the need for all the circuits to have a high integrity earth.
 
By splitting the ring into radials you would be at risk of having higher leakage so no. Could keep cpc as ring, but in reality, the best way to go would be 4mm seperate clean earth throughout.
The price to install is surely justifiable to avoid future nuisance tripping.
 
The OP has stated in his opening post that he has a measured Earth Leakage of 26 mA regulation 543.7.2.201 clearly states that Final circuits feeding socket outlets or connection units, where the pcc in normal service is likely to exceed 10mA then they require a high integrity cpc, the cpc of a Radial circuit should be in the form of a ring, and if the circuit is in metallic conduit or metallic trunking an extra cpc should be installed.
Diagrams depicting this can be found in the 18th edition OSG Page 87, the I have to disagree with essex ensuring the size of the cpc is not sufficient in my book.

My point was FI is not appropriate as the op knows all the details. Would you code it differently to a C3?
 

Reply to High Integrity Earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top