TNS system
60947-2 main switch
60898 double pole 63amp MCBs that feed some caravan boxes now some circuits I can get below the disconnection times of 0.56 ohms but some are 1.22 ohms now I’ve tried changing glands anything else I can do apart from TT the hook up unit? Or do you need upfront RCD

If not change the distribution unit feeding boxes with RCD and Rod it
 
It was never installed right in the first place.

It would be good if the OP could clarify the test results and what they mean by original values. Their other threads recently about this same job make me think these original values refer to the EICR conducted before they started the remedials rather than referring to an EIC.
 
Not changed any glands yet and only going by EICR at the moment, so I’m getting 1.13 ohms on earth loop but if I go to PSC L+N is 0.26 so may get round it that way as will still disconnect in required time, have 63amp 60898 MCB at mains DU then feed the caravan boxes
 
TNS system
60947-2 main switch
60898 double pole 63amp MCBs that feed some caravan boxes now some circuits I can get below the disconnection times of 0.56 ohms but some are 1.22 ohms now I’ve tried changing glands anything else I can do apart from TT the hook up unit? Or do you need upfront RCD

If not change the distribution unit feeding boxes with RCD and Rod it

Not changed any glands yet and only going by EICR at the moment, so I’m getting 1.13 ohms on earth loop but if I go to PSC L+N is 0.26 so may get round it that way as will still disconnect in required time, have 63amp 60898 MCB at mains DU then feed the caravan boxes

You're contradicting yourself.

PSC L+N is 0.26 so may get round it that way as will still disconnect in required time

What do you mean by this then?
 

Reply to High TNS readingssssss in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
727
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top