Hi James.
Sounds like you will need an Electrical Installation Certificate for each one of those jobs.
You can download certificates from the IET website or you should be able to buy them in the wholsalers i.e Robin own brand or Kewtech etc etc.
NIC will also sell you the green certificates I think you mean.
With regard to your PFC, this is in relation to your Ze as the impedance of the earth fault path will restrict the amount of fault current that will flow.
So with the Voltage of 230V and Ze of 2100 - 230/2100 = 0.11A, which isn't enough to cause your MCB/fuses to operate in the required time before the safe touch voltage of 50V is exceeded!!!! so that's why RCD protection is needed on TT system...I hope you have RCD there as you are in quite a bit of danger if not.
You really need to get the Ze (Ra) down to below 200ohms ASAP and RCD if not already present.
HTH
Sounds like you will need an Electrical Installation Certificate for each one of those jobs.
You can download certificates from the IET website or you should be able to buy them in the wholsalers i.e Robin own brand or Kewtech etc etc.
NIC will also sell you the green certificates I think you mean.
With regard to your PFC, this is in relation to your Ze as the impedance of the earth fault path will restrict the amount of fault current that will flow.
So with the Voltage of 230V and Ze of 2100 - 230/2100 = 0.11A, which isn't enough to cause your MCB/fuses to operate in the required time before the safe touch voltage of 50V is exceeded!!!! so that's why RCD protection is needed on TT system...I hope you have RCD there as you are in quite a bit of danger if not.
You really need to get the Ze (Ra) down to below 200ohms ASAP and RCD if not already present.
HTH