I was testing earth rod couple weeks ago at 463 ohms and rcd wouldn't trip couldn't work it out, rammed another rod in and it then started tripping albeit just inside the limit. But on my assessment he said 1660 is the max 200 is only an advisory
 
These readings seem v high, maybe it's the soil type where you are, I'm in south east and even with a meter long skinny rod, the highest reading I've ever got is 86 ohms, it averages around 20/30 ohms, the best ever being 13 ohms, I usually try to install a 2 meter rod but have to cut it short sometimes as It will not go any deeper, I pilot it with a meter long 12mm sds bit first then use a paving mallet, been looking at the dewalt rod driver lately though!
 
These readings seem v high, maybe it's the soil type where you are, I'm in south east and even with a meter long skinny rod, the highest reading I've ever got is 86 ohms, it averages around 20/30 ohms, the best ever being 13 ohms, I usually try to install a 2 meter rod but have to cut it short sometimes as It will not go any deeper, I pilot it with a meter long 12mm sds bit first then use a paving mallet, been looking at the dewalt rod driver lately though!

I personally wouldn't go to the expense of a dedicated rod driver. A half decent SDS drill with a rotary off position will be more than adequate for the needs driving up to 3 X coupled 5/8'' 1m rods!! You can make your own, or purchase an SDS tool to fit the driving nut. Apart from anything else, using an SDS unit will give you an easier drive and far better results. Using a club/sledge hammer will have the rod springing and flexing all over the place, and ending up with the top of the rod sitting in a hole 10X the diameter of the rod ...lol!!

As i have stated many times now, the use of a single 1m rod of any diameter will in 99% of times leave you with an unstable rod. A rod needs depth to achieve stability....
You'll stand a far better chance of going down the full depth of 2X coupled if you stay well away from building external walls (at least 1 or 2m), ...as that's where you'll find all the old building rubble the original builder buried...lol!!!
 
I personally wouldn't go to the expense of a dedicated rod driver. A half decent SDS drill with a rotary off position will be more than adequate for the needs driving up to 3 X coupled 5/8'' 1m rods!! You can make your own, or purchase an SDS tool to fit the driving nut. Apart from anything else, using an SDS unit will give you an easier drive and far better results. Using a club/sledge hammer will have the rod springing and flexing all over the place, and ending up with the top of the rod sitting in a hole 10X the diameter of the rod ...lol!!

As i have stated many times now, the use of a single 1m rod of any diameter will in 99% of times leave you with an unstable rod. A rod needs depth to achieve stability....
You'll stand a far better chance of going down the full depth of 2X coupled if you stay well away from building external walls (at least 1 or 2m), ...as that's where you'll find all the old building rubble the original builder buried...lol!!!

Will give that a try!!
 

Reply to High Ze on a TT system - help for a newbie please..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
983
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
411
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top