i wasn't testing that cable myself, it was a 3 phase cable, one of the phases had the high 80 ohms. cable size is 4mm and long runs, type is SY, perhaps 100 mtrs to a distribution board. Zs from the distribution board ok at something similar to .35 ohms. then another 125 mtr run in 125mm cable to the supply. Ze .35 ohms at the supply
Ok just to satisfy my curiosity I've done a rough calc and in order to obtain a Zs of 80 ohms without any circuit faults for a 4mm+4mm SY cable and your Zdb of 0.35ish as you say, the length of run would have to be around 230M. Does this sound right as a length of run to you???
The only thing that springs to mind is that the engineer was aware of this but rather than sort out what is obviously a problem he took the easy way out and gave additional protection via a 30mA RCD. A cop out in my book in this instance.
But that's only for one phase, the other two are 4 ohms! I suspect a high resistance joint or damaged cable myself.
Thats the point I was making.....for the other 2 to be 4ohms and 1 @ 80ohms, obviously an issue there somewhere as no-one in their right mind would install a 4mm radial @ 230M.
Poor work indeed.
But it's ok because theres an RCD on the circuit.....I've never heard such horse **** in all my life. There is obviously a serious issue there somewhere, one that needs addressing ASAP.
Ok just to satisfy my curiosity I've done a rough calc and in order to obtain a Zs of 80 ohms without any circuit faults for a 4mm+4mm SY cable and your Zdb of 0.35ish as you say, the length of run would have to be around 230M. Does this sound right as a length of run to you???
The only thing that springs to mind is that the engineer was aware of this but rather than sort out what is obviously a problem he took the easy way out and gave additional protection via a 30mA RCD. A cop out in my book in this instance.
The only thing that springs to mind is that the engineer was aware of this but rather than sort out what is obviously a problem he took the easy way out and gave additional protection via a 30mA RCD. A cop out in my book in this instance.
An engineer indeed![]()