In this scenario you have two options.

1. To encase the complete cable run in material that will contain any fire risk that may occur from the OCPD not tripping in time.

2. To install RCD protection to the cable as RCDs have far higher maximum permitted Zs values.

The first option is not really an option due to cost so this only leaves the second option. A 500mA RCD has a max permitted Zs of 100 ohms so I would advise installing one of these at the supply end of the cable.

If you are doing an EICR I would code it as a C2 if there is currently no RCD protection on the cable.

Funnily enough it is in metal trunk all the way to the DB.
Think I’ll speak to my QS about the RCD option.

Many thanks for the advice.
 
Funnily enough it is in metal trunk all the way to the DB.
Think I’ll speak to my QS about the RCD option.

Many thanks for the advice.

It would need to be isolated from other cables so in its own trunking. You would also need to consider down time of supply. Personally I would stay away from this option and install a 500mA RCD.
 
Another option would be to change the OCPD from a 60898 to a BS88. BS88 would have a max permitted Zs of 0.66 ohms. Feeding DBs from DBs is never a good idea.

This is assuming there is access to a bus bar chamber though.
 
Can you not put the Main Tails into Henley blocks and install a 60A Fused Switch as previously stated.

I understand some schools this will not be possible due to the cables coming from an outside substation into a panel board. However with your Ze of 0.35 I would assume the school is not large enough for its own transformer and sub.
 
S type rcd to protect the sub mains perhaps?
Assuming that you still will achieve short circuit protection with the C type mcb
 

Reply to High Zs on submains and high Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
419

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top