Victorian house - just rewired.

EIC provided .......

Description of works "total rewire of all circuits. Dead tests only"

Speechless

Rant over..................
 
re working "live"

plugging in your MFT to a socket to test the Zs is no different than plugging in your mobile phone charger ..................

It’s very different, the mobile phone charger is an appliance connected between L and N, if it’s not done correctly the phone won’t charge.
The tester is deliberately passing a current via the cpc, if it’s not done correctly (dead tests passed, cpc properly connected to the means of earthing) it can cause a lethal voltage to appear on exposed parts connected to that cpc.
 
What a load of tripe from some on here. If some stopped the constant, boring NICEIC bashing and focused on the real issue perhaps matters would be clearer.
NICEIC area engineers certainly encourage contractors to minimise the use of “live” testing wherever practical, simply to reduce risk of harm, eg live tests at a ceiling rose, as dead tests will prove the existence of a cpc, polarity etc. Is plugging in a tester to measure Zs a live test.... of course it is but it presents no risk to the person carrying out the test.
I totally agree that some people/organisations use the H&S card too frequently, but our area engineer is certainly not one of them.
Is live testing the same as live working????
As for the OP, I would certainly be querying the EIC, especially if the installation has rcds/rcbos.
 
In Certsure's Magazine Winter 2017-18 issue ... It finishes with a section on EaWR 1989 & live testing, and a section headed Conclusion 'and where conditional rating is applicable, it follows that carrying out an unnecessary test to determine the prospective fault current at the origin, or indeed elsewhere in the installation, is unjustified live working and hence could be seen as a breach of Reg 14 EaWR 1989'.
Thanks for posting @Midwest :)
I have 2 thoughts - pfc testing is to establish less than 16kA and 6kA (MCB for example) and DNO only comment on 16kA at source. Note they do not certify it's less than 16kA so we test it where that is possible. Or have I missed something?
Next one - saying pfc tests "could be seen as a breach of reg14" is akin to saying my butt "could be seen" as attractive, but that is also unlikely :)
 
If I try to enquire ze from the DNO for tncs they will say 0.35 ohms which is ridiculous and may lead to unnecessarily larger cables installed for circuits to comply with ADS
Maximum should be 0.35 Ohms for PME, 0.8 Ohms TNS but I seem to think some DNOs have revised PME maximum to 0.20 Ohms for new connections.
 
The 0.35 reading is for single phase supplies and three phase up to 200 amps, after 200 amps in three phase the reading is lower and might well be 0.20
 

Reply to How can anyone think this is acceptable ... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
Replies
3
Views
198
It won't be notifiable though as its not a new circuit, if you change the the tails from 16mm to 25mm is that notifiable? No, if you add an...
Replies
5
Views
461

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top