How do I wire a 3-way Zooz Zen21 smart switch? | on ElectriciansForums

Discuss How do I wire a 3-way Zooz Zen21 smart switch? in the USA Electrical Forum area at ElectriciansForums.net

myCharlie

DIY
Joined
Dec 21, 2024
Messages
5
Reaction score
0
Location
Wisconsin
The following dead-end 3-way wiring diagram shows my current setup with the Zooz Zen21, but it's not working. This wiring works fine with a simple standard paddle 3-way switch that doesn't require a neutral wire. However, since the Zooz switch requires a neutral wire, I ran a white wire from the capped neutral wire from the breaker and the light switch to the neutral slot in the Zooz, but it didn't work. Is there another way to get the Zooz switch to work? Thank you in advance.
[ElectriciansForums.net] How do I wire a 3-way Zooz Zen21 smart switch?
 
TL;DR
How do I wire dead end 3-way switch with Zooz smart switch zen21?
The following dead-end 3-way wiring diagram shows my current setup with the Zooz Zen21, but it's not working. This wiring works fine with a simple standard paddle 3-way switch that doesn't require a neutral wire. However, since the Zooz switch requires a neutral wire, I ran a white wire from the capped neutral wire from the breaker and the light switch to the neutral slot in the Zooz, but it didn't work. Is there another way to get the Zooz switch to work? Thank you in advance.
View attachment 119134
Try switching your travelers, other than that it looks like it should work
 
Try switching your travelers, other than that it looks like it should work
To simplify everything, I ignore the second switch in the garage and just use the Zooz switch to try to turn on the light switch. I have the following wiring and it's not working. I have tried the Zooz Zen72, Zen21, and the Kasa HS200 single pole switch. All of these smart switches that requires the neutral is unable to turn the light on with the following wiring diagram.
[ElectriciansForums.net] How do I wire a 3-way Zooz Zen21 smart switch?



However, if I did the same thing with the standard paddle switch but this time capped the neutral wires together since the standard paddle switch does not require a neutral wire. It works perfectly fine with this wiring.
[ElectriciansForums.net] How do I wire a 3-way Zooz Zen21 smart switch?

So, what's wrong with my wiring on the smart switches? Why are all of them not able to turn the light on?
 
Last edited:
The only thing I can suggest is that perhaps the neutral wire you are running to the smart switch isn't working!
With the direct switching that works, the neutral is already provided at the light, so you're just switching the hot.
When you connect the various smart switches, if the neutral you connect to them isn't actually there, they probably won't do anything.

Do you have a multimeter to measure what's going on?
 
The only thing I can suggest is that perhaps the neutral wire you are running to the smart switch isn't working!
With the direct switching that works, the neutral is already provided at the light, so you're just switching the hot.
When you connect the various smart switches, if the neutral you connect to them isn't actually there, they probably won't do anything.

Do you have a multimeter to measure what's going on?
Yes, I do have a multimeter. What do I need to measure? When I turned on the light, there is electricity flow to the light but the light is not turn on.
 
Last edited:
Yes, I do have a multimeter. What do I need to measure? When I turned on the light, there is electricity flow to the light but the light is not turn on.

Do you have a multimeter to measure what's going on?
On the Zooz Zen72 switch:
When the switch is off: Neutral to Load = 0.066v
When the switch is on: Neutral to Load = 3.340v

When the switch is on, the load wire does have power and vice versa.
 
On the Zooz Zen72 switch:
When the switch is off: Neutral to Load = 0.066v
When the switch is on: Neutral to Load = 3.340v

When the switch is on, the load wire does have power and vice versa.
Both those states are “off”
An on signal would be over 100v
Are you sure your meter is set to measure ac voltage?
 
Yes, I do have a multimeter. What do I need to measure? When I turned on the light, there is electricity flow to the light but the light is not turn on.
I was going to suggest you measure the ac voltage on the Zooz neutral terminal with respect to ground, with the switch off and then on. There shouldn't be much voltage, say ~ 1V (if that) in both cases.
Just suggesting you check the Zooz neutral terminal is actually neutral!

And just to say the wiring you show in post #1 is not consistent with the ZEN21 instructions.
But this may not be the only problem.
The regular switch only used two wires in all the Zooz documentation I can see.

Is it possible that the actual source of power for this light is at the regular 3-way switch, and what you are assuming is power at the Zooz is actually a traveller to the other switch?

[ElectriciansForums.net] How do I wire a 3-way Zooz Zen21 smart switch?
 
Last edited:
I was going to suggest you measure the ac voltage on the Zooz neutral terminal with respect to ground, with the switch off and then on. There shouldn't be much voltage, say ~ 1V (if that) in both cases.
Just suggesting you check the Zooz neutral terminal is actually neutral!

And just to say the wiring you show in post #1 is not consistent with the ZEN21 instructions.
But this may not be the only problem.
The regular switch only used two wires in all the Zooz documentation I can see.

Is it possible that the actual source of power for this light is at the regular 3-way switch, and what you are assuming is power at the Zooz is actually a traveller to the other switch?

View attachment 119146

Zooz switch off:
Line to Load = 121.2v
Line to Neutral 121v
Load to Neutral = 0.066v
Load to Ground = 0.0073v
Neutral to Ground = 0.009v

Zooz switch on:
Line to Load = 116.3v
Line to Neutral = 121v
Load to Neutral = 3.382v
Load to Ground = 3.349v
Neutral to Ground = 0.012v

I know for sure that the other switch and the light is not the source of the power. I've measured the voltage of those wires already.
 
Last edited:
Zooz switch off:
Line to Load = 121.2v
Line to Neutral 121v
Load to Neutral = 0.066v
Load to Ground = 0.0073v
Neutral to Ground = 0.009v

Zooz switch on:
Line to Load = 116.3v
Line to Neutral = 121v
Load to Neutral = 3.382v
Load to Ground = 3.349v
Neutral to Ground = 0.012v

I know for sure that the other switch and the light is not the source of the power. I've measured the voltage of those wires already.
could you please take a picture of the paper sheet that came with the Zooz switch
 
Zooz switch off:
Line to Load = 121.2v
Line to Neutral 121v
Load to Neutral = 0.066v
Load to Ground = 0.0073v
Neutral to Ground = 0.009v

Zooz switch on:
Line to Load = 116.3v
Line to Neutral = 121v
Load to Neutral = 3.382v
Load to Ground = 3.349v
Neutral to Ground = 0.012v

I know for sure that the other switch and the light is not the source of the power. I've measured the voltage of those wires already.
It's clear from your measurements that the Zooz switch is not switching power on, it's giving ~3V rather than 120!
Did you have anything in the 'traveller' terminal when doing the above measurements?

I don't have an explanation yet, but yet another question/suggestion:
Do you have a table lamp or lead light that has a plug you could remove, and put the bare ends of the wires into the 'load' and 'neutral' terminals of the Zooz, just to confirm that the simplest of circuits does work.
If it doesn't, I can only suggest that both Zooz products have failed for some reason, or the wiring is somehow different from drawn.
 

Reply to How do I wire a 3-way Zooz Zen21 smart switch? in the USA Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

brilliant thanks for your support. Lee
Replies
8
Views
679
thank you so much. that worked out. i ended up shorting the live switch and sparks flew, but i recovered and its all working now. :)
Replies
3
Views
202

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician Laws and Regulations related to Electrics and Electricals within the United Kingdom. Electrician talk, questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top