Definitely just the one for me.. and that doesn't include getting all the paperwork completed!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss How many EICRs in a day? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I still question that regardless of the limitations etc ... areed with the client (who one assumes is not electrically competent) you as an electrical competent inspector are signing off a satisfactory report (again assuming its satisfactory!!) in the knowledge that everything has not been fully tested & inspected and its effectively worthless for electrical safety?. Does this constitute giving the client the 'professional' impression that the limitations are OK and the premises are safe (satisfactory for continued use)?. I would have thought as a minimum it questions the professional integrity of the inspector in doing it and issuing a worthless piece of paper?.
I would say Badged01 that the inspector must take all of the blame, he/she is the person carrying out the inspection, his/her names are on the certificate after they are signing to say that the results are true. I agree with you, until something dreadful happens, and these scams are highlighted we will never know, we've had part P because something happened, whats next Part EICR? The muppets in charge of things in Government, or whatever, must act NOW, not bury their heads in the sand, thinking about how much more they can claim on their third home, get someone who is of sound technical knowledge, that it's not all about "lets just get a man in" believe that's how these Dilberts see us tradesmen, someone in dirty clothes, I know I've worked with them, they have no inkling of whats required to do any job properly, most of them are toffee nosed and have not a clue. RANT OVER sorry about thatI agree and a fear that like a lot of electrical matters, until something goes terribly wrong and is addressed in a court of law we won't know the answer to 'liability' for an incomplete or heavily limited EICR! Is it purely down to the customer or does the inspector have some blame?
i guess its just as well that he wouldn`t have to then.At 2 hours for perhaps 5 or 6 circuits, you can't hope to test all of them anywhere near properly, and will have to skip a lot of the tests.
For example, a socket RFC, you won't have time to cross connect L-E and measure R1+R2 at each outlet - probably Zs measurements and IR tests are all you can do. And you maybe won't even have time to start disconnecting cables at the CU to measure IR for individual circuits, it will be a global measurement.
So then either you have a lot of LIMs on the test sheet (I've seen this) or instead you start making the numbers up (I've seen this too).
But what if you just measure Zs at the sockets and the results suggest a broken ring? Or the global IR tests are low and you need to find out which circuit is causing this? And there is no time to test fully.
I agree and a fear that like a lot of electrical matters, until something goes terribly wrong and is addressed in a court of law we won't know the answer to 'liability' for an incomplete or heavily limited EICR! Is it purely down to the customer or does the inspector have some blame?