current - 16amp mcb 2.5 radial going through a dp switch 20a which feeds another dp switch 20a which then feeds the two thermostats within immersion ,
i was called because breaker was tripping , immersor pulling 26amps overloading 16amp mcb thus tripping.
immersion system is on the normal side of the supply and not off peak.
i plan on giving immersor two seperate radial feeds , top and bottom thermostats
two seperate spurs and having it on off peak side , there is currently no boost function available.
anyones thoughts
i was called because breaker was tripping , immersor pulling 26amps overloading 16amp mcb thus tripping.
immersion system is on the normal side of the supply and not off peak.
i plan on giving immersor two seperate radial feeds , top and bottom thermostats
two seperate spurs and having it on off peak side , there is currently no boost function available.
anyones thoughts