G

glasgospark

current - 16amp mcb 2.5 radial going through a dp switch 20a which feeds another dp switch 20a which then feeds the two thermostats within immersion ,

i was called because breaker was tripping , immersor pulling 26amps overloading 16amp mcb thus tripping.

immersion system is on the normal side of the supply and not off peak.

i plan on giving immersor two seperate radial feeds , top and bottom thermostats
two seperate spurs and having it on off peak side , there is currently no boost function available.


anyones thoughts
 
It supplies both off peak element and boost element (but not at same time) - it has 2 flex out options, one for each.
The off peak output is controlled by the timer, the boost is 24hr.

You probably know this (apologies if you do) but ALL the house is on cheap rate at night so your supply just needs to be timed to heat off peak element at night.
 
It supplies both off peak element and boost element (but not at same time) - it has 2 flex out options, one for each.
The off peak output is controlled by the timer, the boost is 24hr.

You probably know this (apologies if you do) but ALL the house is on cheap rate at night so your supply just needs to be timed to heat off peak element at night.

thanks mate looks Like best way forward any suggestions on what one to use
 
Try this
Economy 7 Digital Timeswitch + Boost Control

One thing though, are you sure that there isn't one already there? perhaps somewhere more convenient for users eg kitchen - the DP switch adj to immersion tank may just be used as flex out means.

definte sure theres a dp switch in kitchen marked water heater which feeds another dp switch in cupboard upstair which then has two t&e coming from it each feeding a heater in the tank which is in loft
 
You should be able to install the timer in the kitchen in place of the DP switch (presumably in the kitchen DP there is twin in/twin out) You just need the feed in and 2 switched loads out of the timer unit (it would appear the cables already run up to the tank) - remember though you will need DP isolation somewhere before the timer.
 

Reply to immersion heater supply set up in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Locked
Thread closed.
2 3 4 5 6 7 8
Replies
110
Views
4K
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
267

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top