now, forgive me if I am reading this wrong, but I am still on holiday, it's warm, and I've had a few.
but from what I've read it seems the customer has a 20a mcb in their kitchen which is tripping.
in order to rectify this, you want to swap for a 32a?

Correct!

Just want to know if that's notifiable? If it is then notifiable work in a kitchen would mean installing RCD protection would it not?
 
1. it's not notifiable as it's not a new circuit. 2. it's optional whether or not you fit RCD> personally i would prefer to fit one if the customer was happy to pay.
 
Correct!

Just want to know if that's notifiable? If it is then notifiable work in a kitchen would mean installing RCD protection would it not?

You seem confused about a great many things. What does it being notifiable or not have to do with the requirements for RCD protection ?
 
1. it's not notifiable as it's not a new circuit. 2. it's optional whether or not you fit RCD> personally i would prefer to fit one if the customer was happy to pay.

Ok. So upgrading the current carrying capacity of a circuit is not notifiable? Really?? Just a MWS then?
 
I'm confused.
kitchen circuit is tripping the 20a mcb, so your solution is to bang in a 32a instead?
have you done any testing at all. if so, what?
as for notifiable- no. as for rcd- your responsibility is to explain to the customer what protection that will offer and let them decide.
 
No, electric work in a kitchen doesn't always need RCD protecting.

Are you a electrician?

I want know if increasing the capacity of a circuit from 20 amp to 32 amp is notifiable. As far as RCD protection goes then if I'm putting new wiring in a special location with no additional protection then I would expect to put in place An RCD.
 
Ok. So upgrading the current carrying capacity of a circuit is not notifiable? Really?? Just a MWS then?

But by replacing a 20A for a 32A you wouldn't be "upgrading the current carrying capacity of a circuit" would you ? As said a few times already..... is the cable suitable for the new size MCB you plan to fit ?
 
since when is a kitchen a special location? if you can reinstate the RFC then do so, then uprate to 32A. if not, leave well alone.
 
I want know if increasing the capacity of a circuit from 20 amp to 32 amp is notifiable. As far as RCD protection goes then if I'm putting new wiring in a special location with no additional protection then I would expect to put in place An RCD.

you would not be increasing the current capacity of a circuit by swapping the 20a with a 32a. you would merely be changing the OCPD.
the only way to alter the CCC of a circuit is to install a new circuit with the relevant size cable and OCPD.
 
you would not be increasing the current capacity of a circuit by swapping the 20a with a 32a. you would merely be changing the OCPD.
the only way to alter the CCC of a circuit is to install a new circuit with the relevant size cable and OCPD.

Thanks.

So if I reinstate the ring then I can upgrade the MCB to 32amp and just issue a MWS. If the circuit requires new wiring which can't fulfil all the conditions of 522.6.101 then Ill insist it requires some form of RCD protection.
 

Reply to the thread, titled "Increase mcb capacity. Notifiable?" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top