dan86
deleted
now, forgive me if I am reading this wrong, but I am still on holiday, it's warm, and I've had a few.
but from what I've read it seems the customer has a 20a mcb in their kitchen which is tripping.
in order to rectify this, you want to swap for a 32a?
Correct!
Just want to know if that's notifiable? If it is then notifiable work in a kitchen would mean installing RCD protection would it not?
1. it's not notifiable as it's not a new circuit. 2. it's optional whether or not you fit RCD> personally i would prefer to fit one if the customer was happy to pay.
Ok. So upgrading the current carrying capacity of a circuit is not notifiable? Really?? Just a MWS then?
No, electric work in a kitchen doesn't always need RCD protecting.
Are you a electrician?
I want know if increasing the capacity of a circuit from 20 amp to 32 amp is notifiable. As far as RCD protection goes then if I'm putting new wiring in a special location with no additional protection then I would expect to put in place An RCD.
you would not be increasing the current capacity of a circuit by swapping the 20a with a 32a. you would merely be changing the OCPD.
the only way to alter the CCC of a circuit is to install a new circuit with the relevant size cable and OCPD.