Can anyone advise on the right way to replace the danfoss tp9000 thermostat and ts2 sensor with the nest. I have attached pictures showing the current setup.
Thanks in advance,
[ElectriciansForums.net] Installing Nest 3
Live, Neutral and earth from the old programmer go to Live and neutral on the heat link. Terminate the earth in terminal block if no earth terminal is available.
Terminal 3 from the old programmer goes to terminal 6 on the heat link (Hot Water Call)
Terminal 4 from the old programmer goes to terminal 3 on the heat link (Heating Call)
To my knowledge, the nest doesn't use the ts2 sensor but if I'm incorrect, someone will let us know :)
neutral and earth go in the neutral and Earth terminals.
Live goes to the live and both relay commons (2 and 5)
The switched lives go to their respective N/O relay terminals (3 for CH and 6 for DHW)
The two wires from the thermostat (unless connecting wirelessly) go to T1 and T2 and are not polarity sensitive.
Then you carry out the usual electrical tests before turning it back on.
Reply to Installing Nest 3 in the Central Heating Systems area at ElectriciansForums.net
The point is that you set up a schedule of what temperature you want at what time and the nest brings the heating on at the right time to achieve...
davesparks
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...