Insualtuion Resistance - individual circuits V bank of MCBs & RCD readings | on ElectriciansForums

Discuss Insualtuion Resistance - individual circuits V bank of MCBs & RCD readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

Motty

Tested each of 9 new circuits in usual way of L.O.C. and IR, all in theory ok ... CCU is a Hagar split-load dual RCD. 1-4 on RCD1 / 5 - 9 on RCD2

Aware that no requirement for "collective" IR on EIC, just individual circuits.

When tested from the outgoing L of the RCD2 to MCB busbar (all MCBs on, RCD off) to the respective N bar, got 0.06 M ohm - fail. Turn off all MCBs, get >999. Then turn on each one (5 to 9) until circuit 9 reveals the sudden drop.

Take out #9 conductors and test again individually (Downstairs Lighting) showing 600-odd M ohm rather than >999Mohm on L-N (L-E and N-E >999M) (All PIR lights have been disconnected before test) Extractor fan for WC connected so switch off at the 3-pole isolator (Assume Test current detecting / shorting / connecting across motor coil / winding) reconnect into MCB, and now L-N up to 100 odd M-ohms. Still concerned LN is lacking behind LE and NE in the readings overall, and had to call it a day at that point.

No fused spurs or neons, no lamps / bulbs, and the individual test without circuit being connected to the MCB is satisfactory, Yet fails (under 1 M ohm) when connected to MCB / RCD. I discounted reading interference from the RCD as the other 4 circuits in this bank all check out (>999) connected. None of it is Live yet (no connection to new property yet) but brain dead after a very long couple of days! ... any thoughts or pointers would be appreciated

cheers
 
Tested each of 9 new circuits in usual way of L.O.C. and IR, all in theory ok ... CCU is a Hagar split-load dual RCD. 1-4 on RCD1 / 5 - 9 on RCD2

Aware that no requirement for "collective" IR on EIC, just individual circuits.

When tested from the outgoing L of the RCD2 to MCB busbar (all MCBs on, RCD off) to the respective N bar, got 0.06 M ohm - fail. Turn off all MCBs, get >999. Then turn on each one (5 to 9) until circuit 9 reveals the sudden drop.

Take out #9 conductors and test again individually (Downstairs Lighting) showing 600-odd M ohm rather than >999Mohm on L-N (L-E and N-E >999M) (All PIR lights have been disconnected before test) Extractor fan for WC connected so switch off at the 3-pole isolator (Assume Test current detecting / shorting / connecting across motor coil / winding) reconnect into MCB, and now L-N up to 100 odd M-ohms. Still concerned LN is lacking behind LE and NE in the readings overall, and had to call it a day at that point.

No fused spurs or neons, no lamps / bulbs, and the individual test without circuit being connected to the MCB is satisfactory, Yet fails (under 1 M ohm) when connected to MCB / RCD. I discounted reading interference from the RCD as the other 4 circuits in this bank all check out (>999) connected. None of it is Live yet (no connection to new property yet) but brain dead after a very long couple of days! ... any thoughts or pointers would be appreciated

cheers

Think I have understood post correctly. Have you tested between circuit 9 Live and all the individual RCD2 side neutrals?
 
Bit confusing, have you disconnected the suspect circuit Line, Neutral and CPC and tried testin just that circuit, as you don't seem to have done that, or am I reading your thread the wrong way?
 
Bit confusing, have you disconnected the suspect circuit Line, Neutral and CPC and tried testin just that circuit, as you don't seem to have done that, or am I reading your thread the wrong way?

He says he has done that and that it tested clear. It only shows L&N fault when connected to N bar.
 
Bit confusing, have you disconnected the suspect circuit Line, Neutral and CPC and tried testin just that circuit, as you don't seem to have done that, or am I reading your thread the wrong way?

Hi both thanks for replys -

Take out #9 conductors and test again individually (Downstairs Lighting) showing 600-odd M ohm rather than >999Mohm on L-N (L-E and N-E >999M)

yes did disconnect individual circuit and retested - the results were ok but fails when reconnected into the MCB ...
 
Not quite fully understanding but if you only get this fault when connected to neutral bar could possibly be borrowed neutral? though you said all lamps were out.

Definitely no loads still connected? loft light, aerial amplifier, outside light etc etc

Can you confirm that all is good when you test the cable alone and separate
 
Not quite fully understanding but if you only get this fault when connected to neutral bar could possibly be borrowed neutral? though you said all lamps were out.

Definitely no loads still connected? loft light, aerial amplifier, outside light etc etc

Can you confirm that all is good when you test the cable alone and separate

He has confirmed this.
 
This may be the RCD (I normally disconnect them for IR).

Hi again

The bank of MCBs 5-8 on RCD2 are fine, its only when i switch mcb9 to on that the IR dropped to 0.06.

Tested across L busbar / RCD terminal to RCD2 neutral bar.

Load of Ext fan is still connected but off at the 3pole isolator, but have'nt physically detached the wires from isolator to fan.

Circuit #9 Live, Neutral and CPC conductors removed and tested individually = LN = 600+MO, LE = >999MO, NE= >99MO

No borrowed neutrals - all new circuits in new build house.

No lamps or neons, no fused spurs, 8 x downlighter connections disconnected at the click-flow connectors.


Meggerman
have you tested between circuit 9 Live and all the individual RCD2 side neutrals one at a time?

no haven't done this - guessing this in case of cross connection with another circuit? ie. borrowed neutral?
 
Hi again

The bank of MCBs 5-8 on RCD2 are fine, its only when i switch mcb9 to on that the IR dropped to 0.06.

Tested across L busbar / RCD terminal to RCD2 neutral bar.

Load of Ext fan is still connected but off at the 3pole isolator, but have'nt physically detached the wires from isolator to fan.

Circuit #9 Live, Neutral and CPC conductors removed and tested individually = LN = 600+MO, LE = >999MO, NE= >99MO

No borrowed neutrals - all new circuits in new build house.

No lamps or neons, no fused spurs, 8 x downlighter connections disconnected at the click-flow connectors.


Meggerman
have you tested between circuit 9 Live and all the individual RCD2 side neutrals one at a time?

no haven't done this - guessing this in case of cross connection with another circuit? ie. borrowed neutral?


Is this with the other MCBs off? If so then definitely RCD
 
additionally following on from testing circuit 9 Live to all neutrals on RCD 2 there are 2 circuits with fused spurs (immersion heater outlet) but I have removed the fuses from the fascia cartridges

Hawkmoon - didnt't try that either ... think my process of logical elimination went to pot ... however the other four MCBs on that RCD seemed fine switched On and connected to that RCD, hence i discounted the RCD at that point.
 
Obviously (if i'm reading this correctly) the problem lies on the lighting circuit, and not knowing what you actually mean by ''PIR lights disconnected'', because if you are testing with the PIR L+N still connected and the lights not, you will still be reading through the sensor. If that's the case, then you'll be lucky if the PIR is still functioning, if your testing at 500V...
 

Reply to Insualtuion Resistance - individual circuits V bank of MCBs & RCD readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
404
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
993
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
357
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top