As did I (I said the whole "installation or part thereof"). Simple installations with no distribution circuits should be tested as a whole.
And I don't agree that it is nonsense.
Recording the Global IR for each circuit ''IS'' 110% Nonsense!! As i have stated earlier above, Global IR tests are fine for a general check(s), but meaningless as far as recording purposes go.
A major reason for circuit IR values being recorded is to determine if the IR value or values over the working life time of the circuit is noticeably degrading, not just to test if it's compliant at each time of testing.
It was drummed into us as apprentices, that you are looking for any ongoing downward tendencies, in order that they maybe investigated and rectified before a categoric failure occurs...
But then if you don't come from a maintenance/industrial based background you wouldn't know that. It seems they don't teach you much about the reasoning behind periodical testing these days, even within the dedicated testing and inspection courses such as 2391 or the latest 2394/95...