That is incorrect. The insulation resistance values quoted are for individual circuits and that is why you record it as such.

I disagree. My understanding is that the reason for the box on the forms next to every circuit was simply to make the form look tidier.

However the Regulations require the minimum insulation resistance of 1 Megohm for the installation/part thereof and not for an individual circuit, therefore the effect of parallel resistances need be considered. In fact, Guidance Note 3 even suggests that insulation resistance should be tested with all circuits in parallel and not individually (except to find the cause of low readings of course).
 
I disagree. My understanding is that the reason for the box on the forms next to every circuit was simply to make the form look tidier.

However the Regulations require the minimum insulation resistance of 1 Megohm for the installation/part thereof and not for an individual circuit, therefore the effect of parallel resistances need be considered. In fact, Guidance Note 3 even suggests that insulation resistance should be tested with all circuits in parallel and not individually (except to find the cause of low readings of course).


If you get a lowish reading on one circuit, say 40 Meg (low but still acceptable) wouldn't it be appropriate to record it individually on the cert?
 
I do more than consider it, I test it!! I don't understand your post, you are saying you disagree but then also saying that GN3 suggests IR tests are done with all circuits in parallel.
 
I would not call 40M/Ohms low IR

It is if new install and all other circs are >200 - I was just making a point that if a circuit is unexpectedly low with no fault then it is right to record it - even if just for future monitoring of insulation deterioration.
 
I use a Metrel and if I do all 3 cores automatically, I get >30

Low IR is less than 2!

Yes but my point was mainly about individual circuit IR readings and the merits of separately recording them on a cert...

Your 'low' IR being < 2 Meg is ok but if you had a reading of say 4 Meg would you not consider that at least a code 3 to be investigated? At least record on the cert?

Or am I misunderstanding the point of your post?
 
Yes but my point was mainly about individual circuit IR readings and the merits of separately recording them on a cert...

Your 'low' IR being < 2 Meg is ok but if you had a reading of say 4 Meg would you not consider that at least a code 3 to be investigated? At least record on the cert?

Or am I misunderstanding the point of your post?
Not a code 3, if I was testing as part of a board change I would comment on it and on an EICR I would recommend a retest in 3-5 years. The BIG issue with IR tests is that so many now seem to be done as L&N to E so the "real picture" isn't disclosed.
 
In fact, Guidance Note 3 even suggests that insulation resistance should be tested with all circuits in parallel and not individually (except to find the cause of low readings of course).

Are you sure you are reading correctly?? If that is actually what is being suggested in GN/3 then get a black marker and black it out because it's WRONG!!

Nothing wrong with conducting a global IR, but you DON'T record the global IR value, on official test record sheets, as the value for every circuit on a DB/CU, that is just plain bonkers!!

Do you know the reason for recording circuit IR values on official test reporting sheets??
 
Nonsense!

IR is tested per circuit, not just once over the whole installation.

On a large installation the parallel resistances of many perfectly healthy circuits could result in a fail on an overall test.
 
1, that regulation says all distribution ccts with final circuits seperately, not the whole installation.

2, that regulation is nonsense!
 
1, that regulation says all distribution ccts with final circuits seperately, not the whole installation.

As did I (I said the whole "installation or part thereof"). Simple installations with no distribution circuits should be tested as a whole.

And I don't agree that it is nonsense.
 

Reply to Insualtuion Resistance - individual circuits V bank of MCBs & RCD readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
408
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
996
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
357
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top