Yes that's that new approved test......Licking Of Conductors
That is incorrect. The insulation resistance values quoted are for individual circuits and that is why you record it as such.
I disagree. My understanding is that the reason for the box on the forms next to every circuit was simply to make the form look tidier.
However the Regulations require the minimum insulation resistance of 1 Megohm for the installation/part thereof and not for an individual circuit, therefore the effect of parallel resistances need be considered. In fact, Guidance Note 3 even suggests that insulation resistance should be tested with all circuits in parallel and not individually (except to find the cause of low readings of course).
I would not call 40M/Ohms low IR
I use a Metrel and if I do all 3 cores automatically, I get >30
Low IR is less than 2!
Not a code 3, if I was testing as part of a board change I would comment on it and on an EICR I would recommend a retest in 3-5 years. The BIG issue with IR tests is that so many now seem to be done as L&N to E so the "real picture" isn't disclosed.Yes but my point was mainly about individual circuit IR readings and the merits of separately recording them on a cert...
Your 'low' IR being < 2 Meg is ok but if you had a reading of say 4 Meg would you not consider that at least a code 3 to be investigated? At least record on the cert?
Or am I misunderstanding the point of your post?
In fact, Guidance Note 3 even suggests that insulation resistance should be tested with all circuits in parallel and not individually (except to find the cause of low readings of course).
I don't understand your post, you are saying you disagree but then also saying that GN3 suggests IR tests are done with all circuits in parallel.
IR is tested per circuit, not just once over the whole installation.
On a large installation the parallel resistances of many perfectly healthy circuits could result in a fail on an overall test.
1, that regulation says all distribution ccts with final circuits seperately, not the whole installation.