Hi have AM2 next week and just need some help, 3 phase TP+N board, two way and intermediate lighting circuit with 3 switches obviously and one light, doing a global IR test, the lighting circuit say is on L1, so I’m testing all other circuits at once too do I have to switch my switches for every one of these tests
L1-L2,L1-L3,L2-L3,
L1-N,L2-N,L3-N,
L1-E,L2-E,L3-E, N-E
 
I'm not sure what the 'official' procedure for the AM2 is but from an electrical viewpoint, you test all permutations of 2 or 3-way switch positions to make sure each of the strappers and the SL get included in the test along with the PL. But they are only associated with whichever phase the lighting circuit is on, L1 in your example. So, if the switch wiring is not present in any accessories with any of the other phases, there would be no benefit changing the switch positions when testing L2 or L3 as the strappers and SL can't be faulted to those phases.
 
I'm not sure what the 'official' procedure for the AM2 is but from an electrical viewpoint, you test all permutations of 2 or 3-way switch positions to make sure each of the strappers and the SL get included in the test along with the PL. But they are only associated with whichever phase the lighting circuit is on, L1 in your example. So, if the switch wiring is not present in any accessories with any of the other phases, there would be no benefit changing the switch positions when testing L2 or L3 as the strappers and SL can't be faulted to those phases.
Ok thanks so if circuit is on L1 I’ll do,
L1-N,L1-E,L1-L2,L1-L3

So say if I do L1-N I’ll do,
Switch 1 ON test
Switch 2 OFF test
Switch 3 ON test then,
Switch 3 OFF test
Switch 2 ON test
Switch 1 OFF test
Then do the same for others
 
Ok thanks so if circuit is on L1 I’ll do,
L1-N,L1-E,L1-L2,L1-L3

So say if I do L1-N I’ll do,
Switch 1 ON test
Switch 2 OFF test
Switch 3 ON test then,
Switch 3 OFF test
Switch 2 ON test
Switch 1 OFF test
Then do the same for others
I haven't drawn it out but you only need to find positions where each of the line conductors will have been zapped.
 
Just sketch out the three switches and draw through the line conductors until all have been covered, those will be your combinations.
 
I have only done it in my head because I just link them together, but one test with them in one position and another with them all switched the other way, am I correct?
 
Ok thanks guys, the lighting circuit is feed to first switch then 3 core between switches then from last switch to ceiling rose so what I’ll do is,
Switch 1 off
Switch 2 on
Switch 3 off then test

Then Switch 1 on
Switch 2 off
Switch 3 on then test

So will I still have to do this for L1-E, L1-N, L1-L2,L1-L3
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Insulation resistance testing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44
Unsolved
--

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Bradley6969,
Replies
44
Views
6,751

Advert

TrueNAS JBOD Storage Server

Back
Top