Hi have AM2 next week and just need some help, 3 phase TP+N board, two way and intermediate lighting circuit with 3 switches obviously and one light, doing a global IR test, the lighting circuit say is on L1, so I’m testing all other circuits at once too do I have to switch my switches for every one of these tests
L1-L2,L1-L3,L2-L3,
L1-N,L2-N,L3-N,
L1-E,L2-E,L3-E, N-E
 
If you follow the switching options on my indication of live conductors diagram then you can see which conductors become live and are therefore part of the IR test at the supply when you operate switches.
I have just looked through them and operating each switch once will cover all cores no matter the wiring method, so perhaps this should be the default approach, though it does mean a lot more tests than I would like to perform. Eight tests as opposed to four or six. However it would ensure accuracy.
3 phase board, lighting circuit on single pole mcb let’s say L1, T+E to first switch 3 core to next switch and 3 core to last with T+E to ceiling rose on last switch, so I will only have to switch the lights when doing the global test on L1-E and L1-N as only T+E feeding switch
 
Sounds like you are about there.
So you have this wiring arrangement
3 way switch wiring 2nd.jpg

I would say this statement "so I will only have to switch the lights when doing the global test on L1-E and L1-N " is correct, however I am not quite sure why you have added "as only T&E feeding switch".
Possibly because the cables between the switches and to the light are not close to the other phases.
 
Sounds like you are about there.
So you have this wiring arrangement
View attachment 38838
I would say this statement "so I will only have to switch the lights when doing the global test on L1-E and L1-N " is correct, however I am not quite sure why you have added "as only T&E feeding switch".
Possibly because the cables between the switches and to the light are not close to the other phases.
Yes what I meant was there’s only one phase to lights so will only need to switch when either L1-N or L1-E
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Insulation resistance testing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44
Unsolved
--

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Bradley6969,
Replies
44
Views
6,751

Advert

Back
Top