Live and Neutral on one clip earth on the other for anything including the little red neon lights that you can remove should do the trick.



Chris

Forgot to mention if SELV or PELV use 250 volts not 500 volts



Chris[/QUOTE

thought because there are transformers which cannot be removed i was testing at 250v
 
Hi egster71, beg to differ with you but this is not a new installation, the lights are on an existing installation and as such CAN have a limitation on the cert:D
Maybe it's just NICEIC then. A consumer unit should be tested as if it's a new installation. Say the wiring's 20 years old and you change the board then the chances are it'll not be tested for another 20 years!!! :eek:

Up to you of course but if at all possible I'll always do it!
 
Hi egster71, like I said "test phase to cpc, then neutral to cpc, on your test cert put "lim" in the phase to neutral box and say in the limitations box that you have tested to regulation 612.3.3, this wil cover you, it is only a limitation on the ir test and has been mentioned on the report, job done. Look up reg 612.3.3 its fine and dandy !.I also agree that a new installation will not under "normal circumstances" have any limitations, normal circumstances being the operative word, cheers no sarcasm intended
Regards Matt Thornton
 
612.3.3 Says Where the circuit includes electronic devices which are likely to influence the results or be damaged, only a measurment between the live conductors connected together and the earthing arrangement shall be made.

So put live and neutral on one clip, cpc on the other and test. @ 250v Correct or not?
 
Pardon my ignorance but is the section which says line/line not for 3 phase which i will not deal with as a domestic installer. I know we class neutral as a line but this section specifies line/neutral ,line/earth, neutral earth.

Line/Line is applicable in domestic single phase................2 way lighting circuits:rolleyes:
 
Line/Line is applicable in domestic single phase................2 way lighting circuits:rolleyes:

Do you not do insulation resistance at the Cu where on lighting you should just have live neutral cpc. making sure all switches are on would be doing the return path from switch to light.
 

Reply to insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
480

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top