Hey all, just doing some tests on a small extension and have a weird issue with IR on lighting circuit, all switches left open as nightmare to strip all lamps, fittings etc.. L&N to CPC not ramping up over 7-15V DC then resetting test !

L-N on 250V or 500V 31-32 Meg
L-E 32.6 Meg
N-E won't go ! Tried all obvious things to remove out of circuit plus new mains smoke detector etc.. but still no good, any ideas ?
Only fed at moment on a B MCB 6A no RCBO etc.. head scratching or feeding something hidden maybe or a fault ?
Thanks.
 
Just pulled related L,N,E from terminals at Cu to test
The 17th Edition requires the cpc to be connected to the Earthing arrangement before conducting insulation resistance tests - therefore the cpc should NOT be removed from the Earth bar. Otherwise a fault to Earth that isn't a fault to the cpc won't be detected.
 
If the neutral is disconnected you don't need the main switch off but with your tester backing off with the L/N to earth test maybe you have a fault. I don't use an mft to understand their quirks, life is too short:D
 
Bit of a hitler the wife
[ElectriciansForums.net] IR Test ? Weird issue N-E only
not another one!
.
 
Tried again today, still at job now searching for any issues ! 32 Meg L-N & L-E but N-E won't test nor will L+N -E with switches closed, open, ufh Rcd spur found and isolated, lamps out & in, dimmers swapped for standard switches, main switch off at cu and only L&N out N bar /
mcb ! Anyone seen this before ? Fault somewhere ? I'm cracking up here
 
Ditch your multi function tester and get yourself a proper dedicated insulation resistance tester:)
I prefer that its me who decides when a test can proceed, not some all singing and dancing modern playtool that is all things to all situations
Just ditched my Fluke and bought a shiny new Megger 1731 on NIC assessors advice ! So would it be likely a stand alone IR tester would do something? As I ditched my seperates for the Fluke !
 
Tried again today, still at job now searching for any issues ! 32 Meg L-N & L-E but N-E won't test nor will L+N -E with switches closed, open, ufh Rcd spur found and isolated, lamps out & in, dimmers swapped for standard switches, main switch off at cu and only L&N out N bar /
mcb ! Anyone seen this before ? Fault somewhere ? I'm cracking up here

Sounds like fun.

How many separate circuits are you talking about?
 
Tried again today, still at job now searching for any issues ! 32 Meg L-N & L-E but N-E won't test nor will L+N -E with switches closed, open, ufh Rcd spur found and isolated, lamps out & in, dimmers swapped for standard switches, main switch off at cu and only L&N out N bar /
mcb ! Anyone seen this before ? Fault somewhere ? I'm cracking up here

So, just break the circuit into sections and home in on the fault.
 
DO NOT fault find using global IR ............ it won't work ( well it might eventually) but its not the way to approach this...

You need patience, a note book and a pen ............. then test each circuit (cpc's connected to CU) one by one then it will be easy............................ and if you find yourself going round in circles, then walk away and go back afresh another day.
 
To be fair I wanted one since company I worked for had 1553 years ago and it was fantastic and this one is a work of art and technologically another universe but this blinking job is driving me bonkers cause it won't let me get a reading L&N to earth or N-E as is refusing to allow 500V or even 100 V test ! Can't see any reason why
 
A couple of late night thoughts :)
Looking at manual, it seems to say current is limited to 2mA during IR measurement. This perhaps means that by 15V the circuit is passing 2mA and the mft stops the measurement. This would imply about 7.5k Ohms resistance N-E. You could try to measure the resistance directly using mft continuity function to confirm, for what it's worth.
Perhaps there is still an appliance connected, a polarity issue?
 
A couple of late night thoughts :)
Looking at manual, it seems to say current is limited to 2mA during IR measurement. This perhaps means that by 15V the circuit is passing 2mA and the mft stops the measurement. This would imply about 7.5k Ohms resistance N-E. You could try to measure the resistance directly using mft continuity function to confirm, for what it's worth.
Perhaps there is still an appliance connected, a polarity issue?
Thanks Wilko, I've been running around disconnecting odd items, any switches with neons etc, tv boosters, anything & everything but not sure what else it could be. I'll try the cont test across N-E Monday cheers
 
Perhaps see what resistance result you get with an autoranging multimeter to give you an idea of what may be happening, but do check that there is no voltage present first.
The manual does say capacitative loads would cause the voltage to rise slower than expected but I cannot see that there would be a capacitor (or enough capacitance in a circuit) across N-E.
Does the MFT not show any error graphic on failed testing?
 
@Soulsurfer, My wife is coming over to Jersey on Sunday visiting family for a week. I have a Martindale IR tester (nearly said Megger). I am happy to lend it to you for the week if you think it would help. She said she is happy to take it for you. PM me if you would like it and we can swap details.
I have a Megger 1721 and sometimes use the old IR tester if peculiar things happen, MFT's do speed up the job but they can waste a lot of time also.
 

Reply to IR Test ? Weird issue N-E only in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
975
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
662
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
942
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
Replies
19
Views
2K
  • Question
If it's a conventional ring just make an educated guess where the mid point is and split it there, and test each leg from the CU. That should...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks