IR Test ? Weird issue N-E only | Page 2 | on ElectriciansForums

Discuss IR Test ? Weird issue N-E only in the UK Electrical Forum area at ElectriciansForums.net

Soulsurfer

-
Arms
Joined
Feb 21, 2013
Messages
623
Reaction score
163
Location
Channel Islands
Hey all, just doing some tests on a small extension and have a weird issue with IR on lighting circuit, all switches left open as nightmare to strip all lamps, fittings etc.. L&N to CPC not ramping up over 7-15V DC then resetting test !

L-N on 250V or 500V 31-32 Meg
L-E 32.6 Meg
N-E won't go ! Tried all obvious things to remove out of circuit plus new mains smoke detector etc.. but still no good, any ideas ?
Only fed at moment on a B MCB 6A no RCBO etc.. head scratching or feeding something hidden maybe or a fault ?
Thanks.
 
Left all mains on to rest of house as they wouldn't have juice off while in there !
Just pulled related L,N,E from terminals at Cu to test
You should have the cpc connected to the earth bar.
 
I still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
 
I still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
You should have the cpc connected to the earth bar.
Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo boo
 
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC

Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo boo
Never isolate the cpc from the main mass of earth.
 
Just pulled related L,N,E from terminals at Cu to test
The 17th Edition requires the cpc to be connected to the Earthing arrangement before conducting insulation resistance tests - therefore the cpc should NOT be removed from the Earth bar. Otherwise a fault to Earth that isn't a fault to the cpc won't be detected.
 
If the neutral is disconnected you don't need the main switch off but with your tester backing off with the L/N to earth test maybe you have a fault. I don't use an mft to understand their quirks, life is too short:D
 

Reply to IR Test ? Weird issue N-E only in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
170
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
646
  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
413

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top