Is RCD needed at both ends of armour feed to outbuilding | on ElectriciansForums

Discuss Is RCD needed at both ends of armour feed to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

C

chrisbwx

Hi - first post.

I am going to carry out a sub main installation from a main CU in the house, to a garage, (15m from main CU to garage sub board).

The CU in the house has no RCD protection.
The garage will have a local TT, and the sub board will have 30mA RCD as main switch.
The SWA cable 10mm2 will come off a 45A type B breaker. The steel wire sheath will be earthed via gland/banjo at main CU earth.

My question is: given that all sockets/light ccts in the garage will have local RCD protection - do I need to upgrade the main CU to include RCD or RCBO on the SWA feed to the garage? My thinking is that if someone stabs through the armour there is no RCD protection for the inner conductors.....

No doubt this question has been asked before and apologies if this is old, old ground but is the first time I have installed this arrangement on an old board with no existing RCD.

I am domestic installer 2 years in.
 
all i'll say is that SWA does not itself require RCD protection, and as above, you should know this if you are carrying out paid work. FFS.
 
yep. why TT if you have a perfectly good TN system existing? i can see this thread turning sour.
 
Hi - first post.

I am going to carry out a sub main installation from a main CU in the house, to a garage, (15m from main CU to garage sub board).

The CU in the house has no RCD protection.
Not an issue, but what is the earthing system at the house?
The garage will have a local TT, and the sub board will have 30mA RCD as main switch.
Will this comply with the regulations & is it an insulated or metal clad board?
The SWA cable 10mm2 will come off a 45A type B breaker.
Not a problem.
The steel wire sheath will be earthed via gland/banjo at main CU earth.
As it should be, what is the house cu (make & construction), Piranha™ Earth Nut & bin the banjo.

My question is: given that all sockets/light ccts in the garage will have local RCD protection
Will this comply with the regulations?
- do I need to upgrade the main CU to include RCD or RCBO on the SWA feed to the garage? My thinking is that if someone stabs through the armour there is no RCD protection for the inner conductors.....
And this is why the thread should be in the DIY section & you my Electrical Trainee need a college course or somebody to hold your hand.

No doubt this question has been asked before and apologies if this is old, old ground but is the first time I have installed this arrangement on an old board with no existing RCD.
If you have "installed this arrangement" on cu's with an RCD then I point you to the above comment.

I am domestic installer 2 years in.
Fair play to you. maybe this whole thread should be given to the DCLG next time they speak to the scheme operators, wonder what Ms Clancey would make of it?

See my red, sorry but you sound out of your depth.
 
main supply earth is TNS, attached to a ropey old bit of builders band.

Ze to the sheath is 0.25.

Was advised by NICEIC engineer that TT is the preferred way to earth any outbuilding supplies. And understanding from regs that if you have potential extraneous conductive parts coming in - in this case they have cold water supply in garage then TT is a must.
 
Like others have asked what is the supply characteristics to the house?
If tncs - the what is the construct of the garage?
Does the garage have any metal services coming into it?

Also like others there are several areas to look at regarding this kind of install and you haven't provided the necessary info and can only assume you are not aware it is needed thus would conclude you get back into your college books and swat up.... i could understand 1 question about the set-up as we all need a little nudging at times but not the several questions you asked as this shows lack of competence.
 
What I meant was the supply is TN-S and using armoured cable for the sub-main.

I wouldn't bother TTing it at the outbuilding end as the Bonding arragement is not as onerous for TN-S as it is for PME/TNC-S, plus I am not a fan of remote RCDs.
 
Last edited:
Fee fy foe fum, I smell the blood of a troll

or someone that knows exactly what they are talking about!

if not, I return my tankard to the bar. Emptied.
 

Reply to Is RCD needed at both ends of armour feed to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
790
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top