I can't find anything related to this in the regs so I probably misunderstood the question. The way I see it the max Zs for any lighting circuit depends on the circuit breaker for that circuit.
Say we have a lighting circuit with 100x36W ceiling lights which gives us a load of 16A, we choose the breaker of 16A type C, so the max Zs for that circuit will be 1.09ohms. Or with the ambient temperature correction factor 1.09 x 1.06 = 1.15
Say we have a lighting circuit with 100x36W ceiling lights which gives us a load of 16A, we choose the breaker of 16A type C, so the max Zs for that circuit will be 1.09ohms. Or with the ambient temperature correction factor 1.09 x 1.06 = 1.15