It's not fine and where do you start when listing the faults???
Extension of the 3 circuits is wrong (should be at the very least inside an adaptable box....i'd crimp/wago rather than chocblok aswell)
No earth sleeving.
Abit unclear as picture is blurred but if one of those circuits is a ringmain (32a mcb feed) then the single 2.5 T&E cable extending it is wrong.
Blank missing in consumer unit
Numerous labels missing
Jubilee clips to extend the main earth?...thats a first for me
no doubt the list will go on when people with sharper eyes have a peek