dandb

I wish I would have taken my camera (I do not have an I phone :))

Anyway went to change a customers CU. All looked ok and quite a straight forward swap. Twin and earth cabling and docs to show rewired 20 years ago.

Anyway I could not have been so wrong.

Took the front cover off to find a whole load of issues.

1st - 16mm earth cable coming from supplier joint (TNS) is going into the main switch N terminal.
2nd - 25mm incoming Neutal is going into a terminal block connecting to a black 2.5mm single cable.
3rd - 2.5mm red cable connected to the Live main switch terminal along side the 25mm live cable.

Hmmmm I thought....managed to chase the 2.5mm cable to a switch on the other side of the wall. I asked the customer about this switch and she said.

'oh yeah thats an interesting question. That switch bypasses the meter but we never use it. I thought it had been disconnected!!!!'

Well well well.

Apparently the customer bought the house a couple of years back and once she did the previous occupant came back to ask for a tree out of the garden that was a wedding anniversary gift. At that time he told her about the switch.


Shoudl I tell the DNO or not? Customer has said she never used it and I have now ripped it out as to install the new CU.

Anyone else come across anything like this?
 

Reply to Just been to change a CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Oh definitely, the amount of tails that I come across in consumer units barely nipped up is staggering, I always tighten them, wait a minute, give...
    • Like
2
Replies
27
Views
2K
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
587
Sounds more positive.
Replies
8
Views
474
It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks...
Replies
2
Views
854

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks