Ketech 65 trips RCD when Zs testing at Light switch | Page 2 | on ElectriciansForums

Discuss Ketech 65 trips RCD when Zs testing at Light switch in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Am I missing something here, Zs readings should be taken at the furthest point which would usually be at the light fitting in this case?
No, mate - You're not missing anything - it was the end of a long day for me, I was getting familiar with the almost brand new KT65, let alone my first full end-to-end test of an installation I'd done. The manual indicated I could take the reading at the switch and I missed the obvious. My fault. -------------- I'm not due back on site till next week, so I'll take the reading then. I SHOULD have copped it when I successfully took RCD trip readings at the same light switch about 20 minutes afterwards on L, N and E, but like I say - I had a brain trip!!! --------------------------------------------------------------------
genuine Thank You to everyone who responded. -------------- KK
 
You can do it with a Fluke - N & E leads to Earth.

Is it just the Kewtech for some reason?

I have a fluke 1653 ,am i understanding right then that you can test for zs at ceiling rose with N & E leads conected to Earth in the ceiling rose and L conected
to L or SW Live :tongue:
 
I am not saying you should, because there is a neutral at the rose

but at the switch it will work and confirm the earth is good.
 
Hmm think i will give that a go ,any more handy tips Geoffsd ,can you tell me the difference between a short and a short circuit sounds dim i no but just need to understand the meaning (still at college) thanks
 
Just to let everyone know - Managed to take quite a few Zs readings at end of lighting circuits now with the Kewtech 65. Pretty easy when you know how! :) - Fairly sure we're not SUPPOSED to, mind ... as in effect it is working live, no?
 
Hmm think i will give that a go ,any more handy tips Geoffsd ,can you tell me the difference between a short and a short circuit sounds dim i no but just need to understand the meaning (still at college) thanks
Sorry ment short circuit and a dead short thanks
 

Reply to Ketech 65 trips RCD when Zs testing at Light switch in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
570
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
999
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
618
Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top