Who on earth is still fitting dual RCD boards

[ElectriciansForums.net] Landlord's EICR query
 
However, on the basis that the CU must be no older than 4-5 years, this should at the very least have a split load board. Therefore I'm giving the installation a C2 on this basis.

Age of the installation does not change the coding on an EICR.

You are reporting on the suitability and safety of the installation for continued use, you are not reporting on absolute compliance with BS7671.

This is why an EICR is not permitted as a substitute for an installation certificate.


A single RCD on the whole installation is something which can be improved upon but is not potentially dangerous in any electrical sense so it is only a recommendation for improvement.
 
Ironically if this was a Wylex rewireable with an upfront RCD I'd probably give it a C3! (Depending on all the other factors involved, of course)

Then you should be giving this the same coding if it is the same situation.

Would you give this same installation a C3 if you had done the EICR without knowing the back story?

I feel slightly aggrieved that I'll essentially be carrying the can, and likely doing the testing for someone else's rubbish board change.

Don't let your emotions change your EICR codings, you need to remain impartial.

You aren't carrying the can for testing someone else's board change, you're not certifying it or accepting any liability for it.
You aren't even reporting on someone else's board change, you are merely reporting on the installations suitability for continued use.

Out of interest, if it weren't an EICR, and you went to a job where someone had had a recent board change but had fitted a single rcd CU, or a plastic CU, or something else that wouldn't raise a C2 but still clearly shouldn't have been done under the current regs, how would you handle it?

I would explain to the customer what I have found and what problems there are and then discuss with them any work which needs to be done or could be done to improve things.
 
There are people on here who have been in the trade way longer than I , but I have noticed over my time that pretty much no 2 sparks do a PIR / EICR the same.
I reckon we could send 5 sparks to the same old house and we would get 5 different lot of findings and 5 very different lots of recommendations / Codes
 
Everyone is missing the point! A CU change is notifiable. Do the EICR , note any discrepancies and send the forms to Building Control with a covering letter and let them sort it out.
Don't rely on the trade body you are registered with to do the notification.Meanwhile tell the agents/landlords what you recommend to put the installation right.
SAFETY COMES FIRST, YOU HAVE A PRIMARY DUTY OF CARE WHICH OVERRIDES EVERYTHING
 
Everyone is missing the point! A CU change is notifiable. Do the EICR , note any discrepancies and send the forms to Building Control with a covering letter and let them sort it out.
Don't rely on the trade body you are registered with to do the notification.Meanwhile tell the agents/landlords what you recommend to put the installation right.
SAFETY COMES FIRST, YOU HAVE A PRIMARY DUTY OF CARE WHICH OVERRIDES EVERYTHING

I don't think anyone is missing the point. We know the CU has been changed at some point, maybe as long as 5 years ago. We also know there may never have been any paperwork issued.
 
Everyone is missing the point! A CU change is notifiable. Do the EICR , note any discrepancies and send the forms to Building Control with a covering letter and let them sort it out.
Don't rely on the trade body you are registered with to do the notification.Meanwhile tell the agents/landlords what you recommend to put the installation right.
SAFETY COMES FIRST, YOU HAVE A PRIMARY DUTY OF CARE WHICH OVERRIDES EVERYTHING
An EICR is to determine if an installation is safe for continued use. You have stated this yourself (in bold). Whether the installation of the CCU had been notified is irrelevant.
All you can do is comment on the current installation's condition, and if required apply codes and/or make recommendations based on improving the safety for continued use. The inspector is not there to police or do anything about it.
 
They wouldn't. But they might be interested in un-notified notifiable works.
In my experience they have little interest in electrical work , how ever they can hold onto a building competition certificate until they get the part p notification. where this comes from or whom it comes from they couldn't give a rats
 
If you C2 all RCD boards then dual RCD boards will be C2 as well , which as you say we would be C2ing a lot of fairly new builds
 

Reply to Landlord's EICR query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
676
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
410

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top