Hi all.

Looking for a bit of advice.
Customer has a new large induction rangemaster cooker with a total power of 14.8kw.
Currently on a Hager board with a 50a b mcb and an existing 6mm cable.
As soon as oven was switched on it tripped the RCD.
Taking diversity into account the cable should be fine.
Is the breaker too large?
Insulation resistance test comes back fine.
Should I try a smaller breaker?
The oven has the potential to pull 60 + amps and they’ve said they want all 3 ovens on and the hob so I’m wondering if it needs it’s own 63a RCD and a 10mm?

I don’t want to stick it on a 40a and have issues later on.
I guess there’s also the potential that the element had gone as well?
 
think he means if the PF is below unity, e.g.0.8 or less. i'd like to know why it might cause rCD tripping though. in this situation, I'd shift the oven onto a 40A RCBO and see if it held.this would eliminate cumulative leakage.
 
think he means if the PF is below unity, e.g.0.8 or less. i'd like to know why it might cause rCD tripping though. in this situation, I'd shift the oven onto a 40A RCBO and see if it held.this would eliminate cumulative leakage.
Yeah me as well but I was being or trying to be diplomatic.
 
Yes figures on the IR test. And test the appliance too. In fact, do that first. After you have corrected the MCB size on that circuit.

Oh hold on. If you are a trained electrician, you really need to check your college notes. You have forgotten some essential basic things.
College notes?
 
Technically speaking 6mm cable of a 50a mcb is a no no , it either needs to be 10mm or reduce the mcb to a 40

But I have seen an experiment done by J.W where he gets some 1.5mm clipped direct cable to draw very near 70 amps for a considerable length of time before starting to smoke.



Back to the OP , my single build in oven has the strange tendency to trip my house rcd from Time to time
 
Last edited:
As an RCD is a current operated device, why would the 'power factor' have anything to do with it tripping? The power factor is related to the cosine of the angle between the voltage and the current.
An RCD operates on earth leakage, Jim, it is not an OCPD!
 

Reply to Large oven tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top