is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs

b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms


cable per meter = 0.03020ohms so 5.38ohms/0.03020=178.1M

does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense
 
Last edited:
i=p/u, not checked your calc. yet, but pleeeeease distinguish between r1,R1, etc. 2 different measurements!!!!!!!!!

also Ze and Zs mixed up mate. being picky i know, but you got to get it right terminology.
 
Last edited:
Circuit length would be limited by the circuit VD in this instance

As a rough guide assuming a load of 5A and a Ct factor of 1 gives a maximum length of 47.5M to comply with the 3% (6.9V) permitted VD.
 
As I said, rough guide.

I used a Ct value of 1 just as an example, which errs on the side of safety when in actual fact Ct will be less than one due to the CCC of 1.5mm T+E and the fact you would be limiting it to a max of 5A when it is capable of carrying more.

Also it is impossible to say what the ambient temperature of the area surrounding the cable will be........is it in an attic, under insulation etc etc, the OSG bases it's values on ideal situations but does make you aware in the notes associated to the particular table.
 
Last edited by a moderator:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

i=p/u

Arms
-
Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
length of cable runs
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
85
Unsolved
--

Advert

Thread statistics

Created
i=p/u,
Last reply from
Chr!s,
Replies
85
Views
22,800

Advert

Back
Top