length of cable runs
i=p/u
is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs
b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms
cable per meter = 0.03020ohms so 5.38ohms/0.03020=178.1M
does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense
i=p/u, not checked your calc. yet, but pleeeeease distinguish between r1,R1, etc. 2 different measurements!!!!!!!!!
also Ze and Zs mixed up mate. being picky i know, but you got to get it right terminology.
Circuit length would be limited by the circuit VD in this instance
As a rough guide assuming a load of 5A and a Ct factor of 1 gives a maximum length of 47.5M to comply with the 3% (6.9V) permitted VD.
As I said, rough guide.
I used a Ct value of 1 just as an example, which errs on the side of safety when in actual fact Ct will be less than one due to the CCC of 1.5mm T+E and the fact you would be limiting it to a max of 5A when it is capable of carrying more.
Also it is impossible to say what the ambient temperature of the area surrounding the cable will be........is it in an attic, under insulation etc etc, the OSG bases it's values on ideal situations but does make you aware in the notes associated to the particular table.
i=p/u,
Chr!s,
TrueNAS JBOD Storage Server
