i=p/u

-
Arms
Joined
Dec 9, 2010
Messages
7,520
Reaction score
816
Location
Northern Ireland
is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs

b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms


cable per meter = 0.03020ohms so 5.38ohms/0.03020=178.1M

does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense
 
Last edited:
ok loads to consider, so if you were wiring lighting circuit 5A, what is the sums you guys would do to dertamine how many rooms you could do?

isit say 4 rooms down stairs lighting circuit.
living room 10 spotlights 50W =500W
hall 1 pendant 60W
kitchen 8 spotlights 50W=400W
utility room i 2 pendants 60W=120W

1080W/230v= 4.7A ib=4.7A
in=6A
it= in/ca 1,ci 1,cg 1,cc 1
it=6a so would use obv 1.5 t&e
then vd is 19 x ib x L

so heres where im wondering what lenth of cable i can use on 1 circuit, do i have to physicaly measure what i need?? hense knowing the length.and does the switch drops add on to this? thanks if im annoying you and you still trying to get through
 
Last edited:
so when you designing a lighting circuit , how do you approach it? ive seen page 45 in the osg would give you 90 meters would this include switch drops aswell???

it says in osg pg 44 5amp on 1.5mm/1mm would go 71m , and i think vd is included

ok loads to consider, so if you were wiring lighting circuit 5A, what is the sums you guys would do to dertamine how many rooms you could do?

isit say 4 rooms down stairs lighting circuit.
living room 10 spotlights 50W =500W
hall 1 pendant 60W
kitchen 8 spotlights 50W=400W
utility room i 2 pendants 60W=120W

1080W/230v= 4.7A ib=4.7A
in=6A
it= in/ca 1,ci 1,cg 1,cc 1
it=6a so would use obv 1.5 t&e
then vd is 19 x ib x L

so heres where im wondering what lenth of cable i can use on 1 circuit, do i have to physicaly measure what i need?? hense knowing the length.and does the switch drops add on to this? thanks if im annoying you and you still trying to get through

The reason why theres a difference between yours and those in the onsite guide is that your calculations are based on all the load at the extremity of the circuit.

Say on your radial(lighting) you have max length based on the load at the extremity, if you evenly distribute the load you can in effect double the max length.

I used a Ct value of 1 just as an example, which errs on the side of safety when in actual fact Ct will be more than one due to the CCC of 1.5mm T+E and the fact you would be limiting it to a max of 5A when it is capable of carrying more.

The Ct will be less than 1 if Ib is less than It.

Also it is impossible to say what the ambient temperature of the area surrounding the cable will be........is it in an attic, under insulation etc etc, the OSG bases it's values on ideal situations but does make you aware in the notes associated to the particular table.

It lists the various ref methods and the ambient required for compliance.
 
just pretend its 30 degrees normal ,no grouping factor, no insulation and no bs3036 fuse or in a duct
to keep it simple..

i just would like to know how you dertamine how long you can run your cables and do switch drops count aswell??

i know you can and do the sums and if your wrong, you can increase the csa
 
Ive got no reference material so some figures may be incorrect.

Take 1.5 mm cable, CCC 20 amp method C, lets assume ref 103 so CCC= 10amp, mV/A/M = 29

MCB = 6 type B, Load = 6 amp

Ct= 0.915

So if we assume 6 amps at the extremity we get, 6.9 x 1000/ 6x (0.914x29) = 43.35.


If we assume the 6 amps is distributed along the circuit then this will increase the max length.

Ill assume a lenght of 86 meters, double the above, and break it down into 12 x 0.5 amp loads, 7.17 meters apart

The first section sees 6 amp, the next 5.5 amp next 5 and so on.

The volt drop would = 7.38 volts

So if we assume 100 watt per light and evenly distribute them you can see how you extend the lenght.

HTH
 

Reply to length of cable runs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
261
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top