evening guys, ive come across lighting in one room of domestic premises that has been supplied from the ring main at some point. the cable coming from the ring is 1,5mm which goes through the switch then on to the 2 x 12V down lights. This is on an EICR I`m doing. There is no chance at all of accessing under the floor boards as there is very expensive oak flooring down every where. I believe that from memory you can use a switched fused spur for functional switching. I could then put in a 5A fuse and the load side of the cable will be protected. My concern though is the piece of 1,5mm from ring to switch? your thoughts on this would be welcome. I see this as no different to taking a spur off the ring for an extra socket etc, or am I forgetting some thing?
 
Because its not the way we usually do it does not make it bad practice.
As stated above the FCU protects the 1.5 against overload. The MCB will still give adequate fault protection (Zs being correct of course!)
 
Could you not fit a fcu with 5a fuse in it next to the socket the 1.5mm is coming from and put the 1.5mm on the load side and a bit of 2.5mm between the socket and fcu next to it.

because it's probably joined into an inaccessible Jb under the oak floor. i'd just bung in an unswitched FCU with a 3A (or 5A) fuse before the light switch.
 
Replace the 1.5 feeding the switch (replace switch with FCU) with 2.5 simples it aint rocket science it's in the OSG plain as the nose on your face, no arguments just do it right the first time as Mike Holmes says.
 
Put it this way, if I carried out a job whereby I fed a FCU with 1.5mm from a ring final and some muppet came arond telling the customer it's bad practice and against regulation blah blah blah... That is SLANDER! Plain and simple! If you then proceeded to charge the customer to replace it that is obtaining money by deception, a criminal offence!

Any of you idiots out there that continue to propagate this myth that somehow the 1.5mm cable isn't protected are talking out of your rear end. I would suggest that you start by picking up a bloody regs book!!!
 
Replace the 1.5 feeding the switch (replace switch with FCU) with 2.5 simples it aint rocket science it's in the OSG plain as the nose on your face, no arguments just do it right the first time as Mike Holmes says.

Why?

Yes look at the guide for a guide (sarcasm), while at the same time ignoring the forward fusing rules (section 434) in the BGB.

Even the picture in App 15 tells us it does not cover other aspects of the design.
 
If I was installing this from scratch I would fuse down at the point of CCC reduction. If it was already present and as described by the OP, I would leave it as it is, there is absolutely nothing wrong with it.
 
I would suggest that you start by picking up a bloody regs book!!!

OK, to continue the discussion I'll try ....... as I understand the regs the C/B is installed to protect the cable, which in this case I read it as a 32A C/B protecting the 1.5mm cable fed off 2.5mm cable. So the 1.5mm cable isn’t being overload protected by the 32A C/B.

But regs do allow that if due to the cable load characteristics it isn’t likely to be overloaded then overload protection isn’t needed --- provided there is fault protection. For the 12V lights connected via a transformer I’ll take this as holding true for overload and the 1.5mm cable is good to use without circuit overload protection.

However, Ive still got to provide fault protection for this 1.5mm cable even though I don’t need overload protection. I’ll assume an RCD so a L/E fault is taken care of but what about a L/N fault? Will the cable hold out before the 32A C/B or DNO cut-out “pops”?. Using the let thro current calc will probably show the 1.5mm cable can handle this energy and is OK to use.

But if it cant handle the fault, how do I now provide fault protection for the 1.5mm cable?
 
Last edited by a moderator:
OK, to continue the discussion I'll try ....... as I understand the regs the C/B is installed to protect the cable, which in this case I read it as a 32A C/B protecting the 1.5mm cable fed off 2.5mm cable. So the 1.5mm cable isn’t being overload protected by the 32A C/B.

But regs do allow that if due to the cable load characteristics it isn’t likely to be overloaded then overload protection isn’t needed --- provided there is fault protection. For the 12V lights connected via a transformer I’ll take this as holding true for overload and the 1.5mm cable is good to use without circuit overload protection.

However, Ive still got to provide fault protection for this 1.5mm cable even though I don’t need overload protection. I’ll assume an RCD so a L/E fault is taken care of but what about a L/N fault? Will the cable hold out before the 32A C/B or DNO cut-out “pops”?. Using the let thro current calc will probably show the 1.5mm cable can handle this energy and is OK to use.

But if it cant handle the fault, how do I now provide fault protection for the 1.5mm cable?

Going round in circles here, see my earlier post. Fault protection will be supplied via the CB.
 

Reply to Lighting circuit taken off ring main somewhere in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

  • Question
Thanks for the advice.
Replies
11
Views
2K
  • Question
Ouch. Danger notice to customer in my book.
    • Like
Replies
1
Views
606

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top