This is a new one on me and not so sure how to tackle it. The customer is extending 3 bedrooms, ive quoted to install new lighting circuit for these rooms.

The existing circuit for the upstairs lighting does not have an earth and due to its routing it will need extending to fit round the shape of the new rooms. This existing circuit is supplying j.b's in the loft that spider to the bathroom, hall, and another bedroom; the customer will not agree to have these rooms rewired in t&e as it means making holes in the ceilings ! (----)

If I bring in a new feed to the existing J'bs how do I stand on reconnecting the existing circuits that dont have a cpc ?? Customer is adamant he dont want existing rewired but he wants the lights back on, I will IR each of these existing lighting circuits, if they pass I was thinking to make a note on the EIC that customer refuses rewire, and then reconnect.
 
Why not give him a copy of Electrical Safety First Best Practise Guide 1 (to reinforce your advice);

https://www.----------------------------/media/1203/best-practice-guide-1-issue-3.pdf

Page 11 gives guidance on connecting existing light circuits, without a cpc. You will note the caveat at indent for domestic or similar premises at 10.7.
 
1. run a new circuit for the new lights. don't touch the old, broken circuit.
2. tell builder to repair the circuit he's cut.
3. EIC for new circuit, with comment that existing circuit needs rewiring.
 
Why not give him a copy of Electrical Safety First Best Practise Guide 1 (to reinforce your advice);

https://www.----------------------------/media/1203/best-practice-guide-1-issue-3.pdf

Page 11 gives guidance on connecting existing light circuits, without a cpc. You will note the caveat at indent for domestic or similar premises at 10.7.
First time I’ve seen this guideline on electrical installations looks very good and will learn from it. I’ve just scanned through it and just not sure on couple things sure I’ll have more questions when I read through it properly. I always tell customers that they need Rcd protection especially with bathroom lighting circuits and also sockets that have potential to be used for outdoor purposes which most people tend to plug in extension lead and use pressure washer, hedge trimmer, lawn mower etc yet the guideline on this page states you don’t necessarily need a board change, Rcd protection. I would disagree and say that you do need to I’m basing this on domestic not commercial and industrial as I understand a lot of machinery does not require Rcd protection one of my main priorities when doing work is that consumer unit is up to standard and Rcd protection is provided as additional protection
 
1. run a new circuit for the new lights. don't touch the old, broken circuit.
2. tell builder to repair the circuit he's cut.
3. EIC for new circuit, with comment that existing circuit needs rewiring.
Run the new circuit to a JB next to the old to supply the new lights, complete and cert. Take pictures of how you left it.

Tell customer you're having nothing to do with the old as it's non-compliant and potentiality unsafe and under no circumstances could you condone taking a feed from the new JB to the old JB.
 
First time I’ve seen this guideline on electrical installations looks very good and will learn from it. I’ve just scanned through it and just not sure on couple things sure I’ll have more questions when I read through it properly. I always tell customers that they need Rcd protection especially with bathroom lighting circuits and also sockets that have potential to be used for outdoor purposes which most people tend to plug in extension lead and use pressure washer, hedge trimmer, lawn mower etc yet the guideline on this page states you don’t necessarily need a board change, Rcd protection. I would disagree and say that you do need to I’m basing this on domestic not commercial and industrial as I understand a lot of machinery does not require Rcd protection one of my main priorities when doing work is that consumer unit is up to standard and Rcd protection is provided as additional protection

This best practice guide, probably needs an update.

I need to read it perhaps. I don’t think you can advise a customer that a CU change is required, because the existing doesn’t meet existing regs, if that’s what your saying?

If a CU hasn’t additional protection, it does not mean it’s not suitable for continued service.
 
This best practice guide, probably needs an update.

I need to read it perhaps. I don’t think you can advise a customer that a CU change is required, because the existing doesn’t meet existing regs, if that’s what your saying?

If a CU hasn’t additional protection, it does not mean it’s not suitable for continued service.
thing is, any work that you do needs to comply with current regs, so if you have a CU that is fit for continued use, but does not provide the protection that your new work requires ( e.g. RCD for bathroom/lighting/buried cables in walls, then you have to provide that RCD protection, either by a standalone RCD just to cover your work, or by upgrading CU.

the latter option may cost more, but will make the whole installation safer.
 
thing is, any work that you do needs to comply with current regs, so if you have a CU that is fit for continued use, but does not provide the protection that your new work requires ( e.g. RCD for bathroom/lighting/buried cables in walls, then you have to provide that RCD protection, either by a standalone RCD just to cover your work, or by upgrading CU.

the latter option may cost more, but will make the whole installation safer.

Yep I do know any new work needs to comply; but I'm just wondering if @Grant1987 is suggesting an existing CU needs updating for an existing install, albeit it would make it safer.
 
I think that we are detracting regarding the RCD protection and will have to assume that this is complied with for the new part of the installation. Has the OP checked to see if all the lights are standard pendants and batton holders (ie. no class 1 fittings), the switch back boxes are the ones with plastic lugs and there are no metal switch plates?
 
I think that we are detracting regarding the RCD protection and will have to assume that this is complied with for the new part of the installation. Has the OP checked to see if all the lights are standard pendants and batton holders (ie. no class 1 fittings), the switch back boxes are the ones with plastic lugs and there are no metal switch plates?
but what have class 2 fittings got to do with RCD protection? RCDs are for additional,protection. in old speak, protection against direct contact with live parts.
 
I think that we are detracting regarding the RCD protection and will have to assume that this is complied with for the new part of the installation. Has the OP checked to see if all the lights are standard pendants and batton holders (ie. no class 1 fittings), the switch back boxes are the ones with plastic lugs and there are no metal switch plates?

Was there earlier, had a talk and now rewiring most of the lighting bar (some) of the switchdrops. The one circuit n the bedroom he refusing to rewire does have a standard pendant and switch, and will put nylon 3.5's in switch. I will make a note on EIC about this; not much else I can do, except walk.
 
Yep I do know any new work needs to comply; but I'm just wondering if @Grant1987 is suggesting an existing CU needs updating for an existing install, albeit it would make it safer.
I’m saying that when I go to property to do work which is why I’m there in first instance if you existing
Yep I do know any new work needs to comply; but I'm just wondering if @Grant1987 is suggesting an existing CU needs updating for an existing install, albeit it would make it safer.
sorry for delayed reply all I’m saying is that when I go to customers property before I carry out work on circuits involved I tell them that because the existing consumer unit does not provide additional protection by way of Rcd then I would need to cover my work by installing one. If the consumer unit is an old one with bs 3036 semi enclosed then I recommend a board change, or even if they have the plug in mcbs which I thought were non compliant due to breaking capacities? I’m not an expert but here to learn and give my opinion I’m probably over cautious with my work but like to clarify with customer before carrying out any work and the costs involved.
 
I’m saying that when I go to property to do work which is why I’m there in first instance if you existing

sorry for delayed reply all I’m saying is that when I go to customers property before I carry out work on circuits involved I tell them that because the existing consumer unit does not provide additional protection by way of Rcd then I would need to cover my work by installing one. If the consumer unit is an old one with bs 3036 semi enclosed then I recommend a board change, or even if they have the plug in mcbs which I thought were non compliant due to breaking capacities? I’m not an expert but here to learn and give my opinion I’m probably over cautious with my work but like to clarify with customer before carrying out any work and the costs involved.
It’s all in the wording.

Clarify to the customer that:

“You need a surtain amount of protection to do a job.”

“At present your installation does not have that protection.”

Then you would go on to say the best means to achieve this protection

“ fitting a new upgraded CU would give you the required protection to do the job.”

Never say to the customer your rewritable fuse board needs replacing because it’s not up to current regs. That is not true. It’s possibly fine and can continue to be used.

It’s just to achieve the required protection on the work your doing that requires an upgrade.

you are not wrong. It’s just you must clarify to the customer clearly why you are recommending a CU upgrade.
 
It’s all in the wording.

Clarify to the customer that:

“You need a surtain amount of protection to do a job.”

“At present your installation does not have that protection.”

Then you would go on to say the best means to achieve this protection

“ fitting a new upgraded CU would give you the required protection to do the job.”

Never say to the customer your rewritable fuse board needs replacing because it’s not up to current regs. That is not true. It’s possibly fine and can continue to be used.

It’s just to achieve the required protection on the work your doing that requires an upgrade.

you are not wrong. It’s just you must clarify to the customer clearly why you are recommending a CU upgrade.
Yes you’re wording is far better than mine. I’m useless on here with my way of explaining things. All that you’re saying here is exactly what I say to my customers which in simple terms your electrical installation is not up to current standards I recommend you bring them up to standard. I don’t just mean with old rewireable fuse boards but the whole electrics in the property I’ll look at everything and don’t like to leave without telling them what is not compliant with current regs regardless of I’m working on that particular circuit things like cooker points over the cooker or socket outlets over draining board. Knowing that I’m the last electrician in that property I like to make sure that I explain all the issues there
 
What’s wrong with a socket over a draining board :)

Actually as I recall, as long as it’s 300mm from the sink edge, it’s fine apparently.

When I did small jobs, most of mine were, I did the install to the latest regs. Much as I would like them to have a rewire or CU replacement, that’s down to the customers decision.
 

Reply to Lighting circuit what to do in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top