This is a new one on me and not so sure how to tackle it. The customer is extending 3 bedrooms, ive quoted to install new lighting circuit for these rooms.

The existing circuit for the upstairs lighting does not have an earth and due to its routing it will need extending to fit round the shape of the new rooms. This existing circuit is supplying j.b's in the loft that spider to the bathroom, hall, and another bedroom; the customer will not agree to have these rooms rewired in t&e as it means making holes in the ceilings ! (----)

If I bring in a new feed to the existing J'bs how do I stand on reconnecting the existing circuits that dont have a cpc ?? Customer is adamant he dont want existing rewired but he wants the lights back on, I will IR each of these existing lighting circuits, if they pass I was thinking to make a note on the EIC that customer refuses rewire, and then reconnect.
 
just put a new circuit to new area ,on the test cert put existing circuit needs rewire ,the end.

Yeh Buzz that would be functional but aint there a caveat in the regs that a new circuit should be sound "all the way round" so to speak.
[automerge]1568146967[/automerge]
just put a new circuit to new area ,on the test cert put existing circuit needs rewire ,the end.

Just re-read that, yeh I see what you mean. If the customer don't agree to rewire then can I do what I said in original post, thanks.
 
Agree with Buzz. All your work must be compliant so a new circuit for your work would be the best way. Cite 132.16 to back yourself up.
Also tell them their 50+ year old wiring is due for a rewire when they get round to it.
 
Ive really recommended a rewire of existing lighting and switch drops but he's not having it full stop, don't know why but hes a problem customer who wont listen. Anyway the existing feed to the loft needs extending to get the lights back on as the builder cut the cable when he demolished the bedrooms. I was not certain on reconnecting this to the existing lights and switches that don't have an earth. Once ive convinced myself what to do I will get customer to sign a disclaimer and reconnect. The circuit is rcd'd and all class 2 at least.
 
Ive really recommended a rewire of existing lighting and switch drops but he's not having it full stop, don't know why but hes a problem customer who wont listen. Anyway the existing feed to the loft needs extending to get the lights back on as the builder cut the cable when he demolished the bedrooms. I was not certain on reconnecting this to the existing lights and switches that don't have an earth. Once ive convinced myself what to do I will get customer to sign a disclaimer and reconnect. The circuit is rcd'd and all class 2 at least.
Might be one worth swerving if they already a problem.
 
This is a new one on me and not so sure how to tackle it. The customer is extending 3 bedrooms, ive quoted to install new lighting circuit for these rooms.

The existing circuit for the upstairs lighting does not have an earth and due to its routing it will need extending to fit round the shape of the new rooms. This existing circuit is supplying j.b's in the loft that spider to the bathroom, hall, and another bedroom; the customer will not agree to have these rooms rewired in t&e as it means making holes in the ceilings ! (----)

If I bring in a new feed to the existing J'bs how do I stand on reconnecting the existing circuits that dont have a cpc ?? Customer is adamant he dont want existing rewired but he wants the lights back on, I will IR each of these existing lighting circuits, if they pass I was thinking to make a note on the EIC that customer refuses rewire, and then reconnect.
Baptism if they keep acting like that give them a ridiculous price and see if they go for it and tell them you have rules you have to go by. If that doesn’t do it walk away
 
Ive really recommended a rewire of existing lighting and switch drops but he's not having it full stop, don't know why but hes a problem customer who wont listen. Anyway the existing feed to the loft needs extending to get the lights back on as the builder cut the cable when he demolished the bedrooms. I was not certain on reconnecting this to the existing lights and switches that don't have an earth. Once ive convinced myself what to do I will get customer to sign a disclaimer and reconnect. The circuit is rcd'd and all class 2 at least.
Give quote to do what you feel is right. If he doesn’t agree walk away.

EDIT: beat me to it megawatt
 

Reply to Lighting circuit what to do in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top