Hi,
could someone tell me how to calculate the actual disconnect time from a log table and where I can find this table for a 6A RCBO made by British General. I need this to get a meaningful CPC CSA using the adiabatic equation.

Many thanks,

g
 
Technically yes but practically I have never done an adiabatic for circuits issuing from the MCB as the fault current is automatically held to the level of the MCB. However, the main earth from the CU to the Neutral terminal where there is no protection, yes I can see the use of the adiabatic there as if the main earth goes meltdown there is a problem. But for 2.5 cable do you really do an adiabatic? What can you do if 1.5mm² is not enough? Thread a thicker cpc up the cable. Sorry If I am being a bit thick here but ready to learn something new.

You are quite right.

For any of the "standard circuits" you don't need to bother with the adiabatic as the cable size versus OCPD is already fine. That really is why using the usual suspects (standard cases, such as Table 7.1(i) from OSG) makes so much sense as it is one of many less things to worry about design-wise!
Is this correct? The reason I query it is table B7 on p132 of the OSG. It shows minimum CPCs for class 3 B and C type MCBs, for different fault current levels.

For example, a B32 at a fault current of up to 3kA has a minimum CPC of 1.5mm. Above that and up to 6kA, it would be 2.5mm - thicker than the usual 1.5mm CPC that you'd typically find on a ring wired in 2.5mm T+E.

Is there something else at play here?

Calculating CPC size using manufacturer's data usually gives a much smaller min. CPC than those listed in table B7, but not always. BG and Contactum, when asked, gave identical data (which I suspect comes from the product standard rather than their own tests) which, when run through the adiabatic, gives the same results as table B7 for the higher 3-6kA fault.
 
Is this correct? The reason I query it is table B7 on p132 of the OSG. It shows minimum CPCs for class 3 B and C type MCBs, for different fault current levels.

For example, a B32 at a fault current of up to 3kA has a minimum CPC of 1.5mm. Above that and up to 6kA, it would be 2.5mm - thicker than the usual 1.5mm CPC that you'd typically find on a ring wired in 2.5mm T+E.

Is there something else at play here?
I think it is down to the ideal case of DB PFC and max let-through of the MCB standard, and the real-world case of MCB generally being better, and the actual PFC being less.

For example, if you have a DB with 6kA PFC (assuming for now 230V) then your Ze is around 0.038 ohm. To bring that down to 3kA you need to double that, and with the R1+R2 of 2.5mm T&E being around 19.5mOhm/m that is 2m of cable.

So for most faults on any real-world installation using typical circuits you won't reach cable-damaging I2t, and if you do it will only be the first metre or so before a very close (and very hard) fault that needs replacing.
 
I think it is down to the ideal case of DB PFC and max let-through of the MCB standard, and the real-world case of MCB generally being better, and the actual PFC being less.

For example, if you have a DB with 6kA PFC (assuming for now 230V) then your Ze is around 0.038 ohm. To bring that down to 3kA you need to double that, and with the R1+R2 of 2.5mm T&E being around 19.5mOhm/m that is 2m of cable.

So for most faults on any real-world installation using typical circuits you won't reach cable-damaging I2t, and if you do it will only be the first metre or so before a very close (and very hard) fault that needs replacing.
Ah, I see, that puts it in perspective!
 
Take a look at the fault curves in appendix 3 of BS7671. For type B and C breakers/RCBOs, if it meets any permitted disconnection time, even 5s for distribution circuits, then it disconnects at 0.1 seconds (or faster). There is no middle ground, as above a certain current the magnetic trip will operate and will disconnect instantaneously. For example, you can't make it disconnect in exactly 1 second.

As you are presumably using a B or C type breaker/RCBO, use the fault current at the origin of the circuit for the calculation. For these devices, let through energy tends to increase with fault current, and fault current is greatest at the origin. This is the most onerous point in the circuit.
Thanks pretty mouth.
 

Reply to log tables for actual disconnect time in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
460
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
374
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
691

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top