Hi,
could someone tell me how to calculate the actual disconnect time from a log table and where I can find this table for a 6A RCBO made by British General. I need this to get a meaningful CPC CSA using the adiabatic equation.
Many thanks,
g
hi yes i do have both and if you are saying i should use fig 3A4 that's ok but i have a fault current of 301A and if I take 0.4 seconds as t then I end up with a cross sectional area of >1.66mm. can I use the lower trip time of 0.1 seconds?Do you have a copy of the 18th edition Regs book or onsite guides?
thanks telectrix but can you tell me how to justify its use? thanks,use 0.1 sec. it's well in @ 301A.
It applies to all protective conductors, except bonding conductorsI think the adiabatic applies to the main earth not cpc.
Take a look at the fault curves in appendix 3 of BS7671. For type B and C breakers/RCBOs, if it meets any permitted disconnection time, even 5s for distribution circuits, then it disconnects at 0.1 seconds (or faster). There is no middle ground, as above a certain current the magnetic trip will operate and will disconnect instantaneously. For example, you can't make it disconnect in exactly 1 second.thanks telectrix but can you tell me how to justify its use? thanks,
g
Strictly speaking it applies to all conductors, it is just the CPC is often smaller than the live to save money as it has little to do normally. Of course if you meet the adiabatic for the CPC then the live conductors will be OK.It applies to all protective conductors, except bonding conductors
Technically yes but practically I have never done an adiabatic for circuits issuing from the MCB as the fault current is automatically held to the level of the MCB. However, the main earth from the CU to the Neutral terminal where there is no protection, yes I can see the use of the adiabatic there as if the main earth goes meltdown there is a problem. But for 2.5 cable do you really do an adiabatic? What can you do if 1.5mm² is not enough? Thread a thicker cpc up the cable. Sorry If I am being a bit thick here but ready to learn something new.It applies to all protective conductors,
You are quite right.Technically yes but practically I have never done an adiabatic for circuits issuing from the MCB as the fault current is automatically held to the level of the MCB. However, the main earth from the CU to the Neutral terminal where there is no protection, yes I can see the use of the adiabatic there as if the main earth goes meltdown there is a problem. But for 2.5 cable do you really do an adiabatic? What can you do if 1.5mm² is not enough? Thread a thicker cpc up the cable. Sorry If I am being a bit thick here but ready to learn something new.