136.4 ohms at lights whilst doing the loop test before we change the board. Guessing they've been lucky ? Plus side is I get to put an earth stake in were see how much I remeber from the one I did 2 years ago
Who the hell in the IET came up with a figure of ≤200Ω wants taking out and shooting at dawn!
How many in the trade have to same attitude as HHD “Oh well, it’s near enough, it’ll do.”
Thats more like it Tony, just like old times :smiley2:
Give me a 'realistic' idea of how to go about getting a sub 1 result and I'll listen Tony? Even with an SDS adaptor you'll still need a HUGE rod to get that sort of figure.
I really would like to hear from you about the following as you will know the answers and I am just talking from theory not from experience:
1. What Ra would you class as acceptable in a domestic situation AND why?
2. How would you achieve this figure taking into account the figures in post 15? (An SDS adaptor and 5m rod is not going to get the Ra below 1Ω)
Also...... Are there ANY electricians on this site who have got <1Ω for a domestic TT installation? Apart from you Trev![]()
Thats more like it Tony, just like old times :smiley2:
Give me a 'realistic' idea of how to go about getting a sub 1 result and I'll listen Tony? Even with an SDS adaptor you'll still need a HUGE rod to get that sort of figure.
........................
Well you're going to have to balance cost and quality. I'd accept <10Ω for a domestic install. Yes you're still relying on the RCD's but it's low enough to not fluctuate from that reading by much, providing a stable system.
Depends where you are in the country 5m may well get you <1Ω. There is always an option of adding another rod if needed.