Joined
Sep 19, 2012
Messages
543
Reaction score
193
Location
SW. London
Testing a ring earlier and found 0.8M ohm at 250v between (L&N) - E.
This wouldnt be a neon causing this would it as im testing between L N (joined) to E ? I have not yet tested between the three individually.

This low reading is making me hope somethings still connected, there is a digital boiler controller that I suspect is wired into the supply side of a FCU but maybe its not; would this cause a low reading like this ? or anything else to bring back 0.8M ! I tested between (L&N) - E. Thanks all
 
Real pain low IRs in a RFC especially in old installations that have spurs all over the place. Finding everything to unplug and/or disconnect can be real fun.

Took me four hours to find a dead short that was tripping the RCD in preference to the MCB.

Much of that time was determining what was and wasn’t in the RFC, what was spurs and what had been spurred off the upstairs RFC.

Then a case of aiming for the middle splitting and repeating until I had, with a degree of certainty, found the section of cable with the faulty on.

As it turned out a drain had split and filled the underfloor with water. There was no way I was going to get under the floors, customer not intrested in the leak, just wanted the power back on ASAP.

Disconnected the suspect cable, Ran a temporary cable from socket to socket, tested the patched up RFC and powered back up, all good.

Got lucky really as no random spurs off the suspect cable.

Finally disconnected the temp cable, put the two legs on 16amp MCBs, tested and powered back up.

Left a quote for reconnecting the RFC in surface mount on a Sunday to have them back up and running.

Not a bad job really but not quick.
 
That's interesting SparkyChick. Have you seen some surge protected devices given poor IR results at 250V? Bit worrying as it means you cant assume it's not a SPD if the reading is low at 250V.

No, just thinking out loud :)

I'm not sure how say metal oxide varistors fail as they age, could they result in low readings at lower voltages than their original?

As I say, just thinking out load, but I'd be looking for things connected at this point and/or breaking the circuit down to try and identify the fault.
 
No spin this was an individual circuit.

Then you have an easier job to do then .........

How many socket circuits in the property?

I was doing a CU change recently and when I tested the "immersion" circuit I got a similarly low reading .................. I found an RCD spur that a plumber had added for a shower pump ................ removed the RCD spur and the readings went over 30 mohms
 
Thats it thou isnt it, customers gonna say well im not sure about that, and im thinkng well it is what it is. Customer needs an extra socket in the loft ready for the cctv guy whos installing Thursday.

Matey ......... this is the real world - if you don't outline potential issues you won't learn ................
 
Then you have an easier job to do then .........

How many socket circuits in the property?

I was doing a CU change recently and when I tested the "immersion" circuit I got a similarly low reading .................. I found an RCD spur that a plumber had added for a shower pump ................ removed the RCD spur and the readings went over 30 mohms

More searching required then it looks like, before surgery.
 
Er 3 I think, but its only 1 that im concerned about atm

So your next step is clearly identify ALL the sockets on each of the circuits, then go hunting for additional connections ............. alarms, TV amplifiers, RCD sockets, RCD spurs, floodlights....................

tedious but has to be done

And if you can't find any extra connections then you need to split the circuit to try and find where the low reading is...
 

Reply to Low insulation reading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
359
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top