Knowing me im reading to deep into the regs but page 27 of the on site guide, the purpose of protective earthing is to ensure that in the event of a fault,line conductor to exposed conductive part sufficiant current flows to operate the protective device in the time required .as we all know. so correct me if im wrong , but there is no earth connection on light switches so when the face plate is screwed back with a solid lug on the back box then if the live wire of the switch breaks off or pops out as the do and touches an unearthed back box it wont blow the protective device but the face plate screws will be exposed and live ,so you can see my point .. unless its an earthed metal face plate then the same should apply as socket outlets because at the end of the day they are back boxes single or double