Is that something new that's come out that as slipped by me without me noticing Nick?
Me too, Nick is quite correct on the '1 fixed lug' part but there is no distinction made between socket and lighting back boxes in BS7671:2008 or Guidance Note 8 (earthing and bonding).
Knowing me im reading to deep into the regs but page 27 of the on site guide, the purpose of protective earthing is to ensure that in the event of a fault,line conductor to exposed conductive part sufficiant current flows to operate the protective device in the time required .as we all know. so correct me if im wrong , but there is no earth connection on light switches so when the face plate is screwed back with a solid lug on the back box then if the live wire of the switch breaks off or pops out as the do and touches an unearthed back box it wont blow the protective device but the face plate screws will be exposed and live ,so you can see my point .. unless its an earthed metal face plate then the same should apply as socket outlets because at the end of the day they are back boxes single or double
The boiler (downstairs in utility) was on the upstairs ring :confused:. Even after taking the bonding out of the equation there is still an extraneous connection (via the pipework itself I guess) giving a better than (I) expected R2.
All in all, was a useful exercise though. Was doing a check prior to changing the CU.
Is someone paying you to find why the r2 reading is so good?
I wish :D, no, this was for my elecsa inspection tomorrow, just me being a bit too picky :rolleyes:
Last minute change of CU as the job I was going to use is going too slow (not due to me though :cool:). Had to pay the LABC £141 for the privilege as well :mad:
... the purpose of protective earthing is to ensure that in the event of a fault,line conductor to exposed conductive part sufficiant current flows to operate the protective device in the time required...
I concur.
Reg 411.3.1.1 "Exposed-conductive-parts shall be connected to a protective conductor....."
couldn't be bothered to type it all in, but you can read the rest for yourselves :)