Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
 
Back to your original question does it have to be <0.05ohms......Im not so sure now, I think it is only a recommendation as dont think there is a Reg No but not too sure.....although your reading is very high and is probably due to what Archy has stated
 
There is no limitation on the resistance (or length) of bonding cables, 0.05Ω is just a suggested ball figure (GN3) to prove the cable 'continuity'. However your reading suggests you have a cable of approximately 137m, very unusual in a domestic installation, but never the less, if correct it would conform to BS7671:2008+A1:2011. If this is not the case your test method or connections are faulty and retesting is advisable. In which case if retesting reveals a similar resistance, further investigation and/or replacement would be necessary as it's likely you don't actually have a continuous length of 10mm[SUP]2[/SUP] cable.
 
Last edited by a moderator:
it goes in the floow at front of property, (there are 3 x 10mm and 2x6mm, one 10mm being gas) one resurfaces under the sink and terminated there but i couldnt tell you if it is continuous, i mean why would you not run it continuous whenn the extension was being built!! grind my gears this does.&nbsp;<br>It is maybe 10-15 metre run to the water pipe in kitchen. so it obviously shouldnt be that high....so considered that, it isnt acceptable as the run is so short? or is that 0.05 only ever a rough guide. I mean 0.3 isnt really that bad surely??
 
Between which two points are you measuring to obtain the reading of 0.25 ohms, the measurement of 0.05 ohms is nothing to do with the length of the main bonding conductors as I see it
 
, the measurement of 0.05 ohms is nothing to do with the length of the main bonding conductors as I see it
You are supposed to verify the continuity of the conductor when disconnected so it is all about the csa and length.

A 10mm² copper conductor less than 27m in length cannot be more than 0.05Ω

0.05 is considered negligible - 0.25 or 0.3 is not.
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top