it goes in the floow at front of property, (there are 3 x 10mm and 2x6mm, one 10mm being gas) one resurfaces under the sink and terminated there but i couldnt tell you if it is continuous, i mean why would you not run it continuous whenn the extension was being built!! grind my gears this does. <br>It is maybe 10-15 metre run to the water pipe in kitchen. so it obviously shouldnt be that high....so considered that, it isnt acceptable as the run is so short? or is that 0.05 only ever a rough guide. I mean 0.3 isnt really that bad surely??
Yes, that is what serpico raised.if as stated 0.05 is used as a guide as its considered negligable then at what value does it become a prob as if that was the case then a stated value would need to be given in bs7671.
i believe voltage drop (50v safe touch) as in supp bonds plays a part in this - 0.05 ohms is good for 27m ensuring no drop +or- 50v will occur between accessible part..
Yes, that is what serpico raised.
.
Yes, but if the conductor is continuous it cannot be that high.So would a resistance of 0.25 Ohms mean that the bonding conductor is unsafe as the resistance is too high in the event of a fault?
So as Geoffsd and Serpico said:
for a 100A domestic supply, the Ia value would be either 1200 at 0.4s or 630 at 5s
To which the higher would make the maximum permittable resistance of the main bonding conductor is 0.041 ohms if R< 50/1200
The cable measured was directly from the conductor at the MET to the bonding clamp using croc clips?
So would a resistance of 0.25 Ohms mean that the bonding conductor is unsafe as the resistance is too high in the event of a fault?
How can you do that?Forget about resistance,
Someone has done that.select the right size job done
Oh.If the bonding conductor is in place and the right size, just test its resistance
But it doesn't - that's the problem.so that it relates to length and csa.
How can you do that?
Someone has done that.
Oh.
But it doesn't - that's the problem.