Main bondage | Page 2 | on ElectriciansForums

Discuss Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 17, 2012
Messages
178
Reaction score
17
Location
London
Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
 
it goes in the floow at front of property, (there are 3 x 10mm and 2x6mm, one 10mm being gas) one resurfaces under the sink and terminated there but i couldnt tell you if it is continuous, i mean why would you not run it continuous whenn the extension was being built!! grind my gears this does.&nbsp;<br>It is maybe 10-15 metre run to the water pipe in kitchen. so it obviously shouldnt be that high....so considered that, it isnt acceptable as the run is so short? or is that 0.05 only ever a rough guide. I mean 0.3 isnt really that bad surely??[/QUOTE]

You are joking with this statement I hope...
 
I know that, but that is not how it's explained in GN3 perhaps that's where people get confused with the 0.05 ohms, apparently that is the most common question people get wrong on testing courses. The max resistance value of a main bonding conductor, we all know it depends on the size of the cable and in this case yes with 10mm that equates to a max length of 27m. However the 0.05 ohms in GN3 refers to testing between any two points such as metallic pipes etc That was my reason for asking which two points he was measuring between.
You are supposed to verify the continuity of the conductor when disconnected so it is all about the csa and length.

A 10mm² copper conductor less than 27m in length cannot be more than 0.05Ω

0.05 is considered negligible - 0.25 or 0.3 is not.
 
It's just that the resistance between two points should be negligible so that there is negligible potential difference between them (in the event of a fault).

0.05Ω is deemed to be negligible as nothing will have a resistance of 0.00Ω.

The fact that this equates to 16m with 6mm², 27m with 10mm² or 43m with 16mm² is not really anything to do with it.
(Although, obviously a 10mm² conductor less than 27m cannot be higher than this and in a 'normal sized' property it will be less.)

If the resistance of the pipe itself (without bonding) to the MET and all other pipes and e-c-ps were less than 0.05Ω then the protective bonding conductor would not be necessary.
 
I agree with all you've typed. My asking where he was testing to and from, as in his domestic situation it seemed as though he was using the 0,05 ohms as a guide for his expected reading of his bonding conductor, I didn't realise he was trying to determine the length of the bonding conductor.
It's just that the resistance between two points should be negligible so that there is negligible potential difference between them (in the event of a fault).

0.05Ω is deemed to be negligible as nothing will have a resistance of 0.00Ω.

The fact that this equates to 16m with 6mm², 27m with 10mm² or 43m with 16mm² is not really anything to do with it.
(Although, obviously a 10mm² conductor less than 27m cannot be higher than this and in a 'normal sized' property it will be less.)

If the resistance of the pipe itself (without bonding) to the MET and all other pipes and e-c-ps were less than 0.05Ω then the protective bonding conductor would not be necessary.
 
You have to use the current required to operate the 100A fuse 1200 @ 0.4s or 1800A @ 0.1s.
50/ 1200 = 0.04Ω

That's used for supplementary bonding and even there the actual conductor has to be <0.05Ω.

Main bonding conductor conductor must be <0.05Ω.
 
My asking where he was testing to and from, as in his domestic situation it seemed as though he was using the 0,05 ohms as a guide for his expected reading of his bonding conductor, I didn't realise he was trying to determine the length of the bonding conductor.
I don't think he is.

In the original question he says

Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
I don't think the length has anything to do with it apart from the physical impossibilities.

 
That's the first time supplementary bonding has been mentioned, as I said where did he get his ohmic value for his main bonding from, where has he measured it to and from............................It's main bonding he has referred to in his question..... did he measure between two pipes, one end of a cable to another, a pipe to a cable I ask again where???
He's using the formula for whether (supplementary) bonding is required but using the wrong numbers.

See above post.
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top