There is no limitation on the resistance (or length) of bonding cables, 0.05Ω is just a suggested ball figure (GN3) to prove the cable 'continuity'. However your reading suggests you have a cable of approximately 137m, very unusual in a domestic installation, but never the less, if correct it would conform to BS7671:2008+A1:2011. If this is not the case your test method or connections are faulty and retesting is advisable. In which case if retesting reveals a similar resistance, further investigation and/or replacement would be necessary as it's likely you don't actually have a continuous length of 10mm[SUP]2[/SUP] cable.