Main bondage | Page 12 | on ElectriciansForums

Discuss Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 17, 2012
Messages
178
Reaction score
17
Location
London
Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
 
I think if we could replace all the wood in all the houses with copper and everything connected together problem solved, mind you how would we be able to sleeve everything..........such a shame wood has not got very low resistance........... then again if we were on the moon we'd have to moon everything lol
 
I think if we could replace all the wood in all the houses with copper and everything connected together problem solved, mind you how would we be able to sleeve everything..........such a shame wood has not got very low resistance........... then again if we were on the moon we'd have to moon everything lol

And if we were on Titan,we would have to Titan the pipes
 
I think if we could replace all the wood in all the houses with copper and everything connected together problem solved, mind you how would we be able to sleeve everything..........such a shame wood has not got very low resistance........... then again if we were on the moon we'd have to moon everything lol

That's where the Yanks have got us beat, they Ground everything.
 
well thats not quite right is it ?
a minimum sized bond conductor is specified , but no upper resistance value needs to be complied with for that conductor if its the correct csa.
ok, but when testing the 10mm2 bonding conductor of unknown length in a domestic setting, it'd be sensible to use some sort of ball park figure for what might be expected to be a reasonable maximum figure in that setting - say 0.05 ohms or 27m of cable rather than just doing the test but saying ah but there's no figure specified in the regs and the cable could be infinitely long, so it doesn't matter what figure you get.

which presumably is where the OSG figure comes from.
 
I think if we could replace all the wood in all the houses with copper and everything connected together problem solved, mind you how would we be able to sleeve everything..........such a shame wood has not got very low resistance........... then again if we were on the moon we'd have to moon everything lol

Faraday cages - homes of the future :)
 
Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>

Sod it, I'm going to have a go at answering this.

The resistance reading for a 10mm2 main bonding cable in a domestic setting should hardly ever be above 0.05ohms, and only if there is good reason to think the cable might be longer than 27m should a reading higher than this be potentially deemed acceptable without needing further investigation.

If the resistance reading is greater than 0.05 ohms with no reason to suspect a cable length longer than 27m, then this would indicate that there is a problem with the cable that means it is unlikely to be 10mm2 for its entire length, and / or has a high resistance joint in the cable, and this should be investigated and rectified, or if that's not possible then a judgement would need to be made about whether the reading is sufficiently high to justify running a new unbroken 10mm2 cable to ensure compliance.

So only in a very limited number of cases should the resistance reading of the 10mm2 cable be higher than 0.05 ohms in a domestic setting, and only in a massive mansion would it be expected to get anywhere close to 0.25 ohms.

or rule of thumb - it should usually be lower than 0.05 ohms in a domestic setting, anything higher usually indicates a problem that should really be sorted out.

That's basically how I see it in the absence of any hard and fast rule from BS7671. Have we been arguing semantics here, or does anyone have a significantly different understanding of the situation?
 
in responce to question, why not 1mm2

if i remember right, doesnt the conducter have to be a minimum off half the incoming tail size (id have to check notes first, forgive me but havent done really any domestic and even that was small alterations)

e.g. 25mm tails

16mm earth.
 
in responce to question, why not 1mm2

if i remember right, doesnt the conducter have to be a minimum off half the incoming tail size (id have to check notes first, forgive me but havent done really any domestic and even that was small alterations)

e.g. 25mm tails

16mm earth.

bonding conductor needs to be min. of 50% of the size of the main earthing conductor, with a min. of 6mm., except with PME< then it's min. 10mm.
 
OK can we get this thread back on track please? the title was main bondage but it seems to have drifted into earthing.
[ElectriciansForums.net] Main bondage
 
Ok , maybe the value is used to ensure all bonding has a resistance of similar value otherwise you could have a diffence in potential.

Checked all books today and as already mentioned it is only refered too as a value between extraneous parts
 
Checked all books today and as already mentioned it is only refered too as a value between extraneous parts
Isn't it (0.05) used wherever a value of negligible resistance or negligible difference in resistance is required?

Testing between joined metal parts for continuity, difference between R1+R2 at various locations on a ring, and of course main bonding continuity between extraneous parts and MET.

It IS a value regarded as negligible.
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top