Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
Within reason, the resistance will obviously be very low.
and its the interpretation of this particular statement that is the cause of opposing views.
the fact that bs7671 doesnt expand on it leaves everyone to draw their own conclusions.
and that is probably the most satifactory end to this debate we're gonna get.
0.05 ohms was mentioned in Op and it was asked "has the maximum value of the main bonding conductor got be below that figure of 0.05ohms" (it's so long ago I think that's what was asked) and all the way through this post I have said NO it doesn't at all. As long as the main bonding conductor is selected with BS7671 in mind 0.05 ohms does not even need to be considered.
that's a cop out answer.
the bonding conductor was already in place, and was being tested to confirm whether it actually did comply being as it wasn't visible for it's entire length so the integrity of the conductor couldn't be verified by visual inspection.
Given that this test has been conducted, what in your opinion should be the maximum acceptable resistance reading for that bonding conductor?
Not at all, I have been trying to educate the poster on the question of the max value of the main bonding conductor, not sorting out his high value, I thought others had pointed him in the right direction regards, joints, reduced cable size hidden and re-joined behind walls or somewhere. As someone said with the reading he was getting it would have to be a very long cable indeed. If he used a wandering lead method he could of obtained an estimate of the length etc................................But THERE IS NO MAX value of 0.05ohms for the main bonding conductor the his measurement has to be below. Reread his question ................. So no not a cop out a FACT
IMO, the resistance measured ( of a main bonding conductor ) should tally with the mohms/m ( in BS7671 and 0SG as 0.0018ohms/m for 10mm) multiplied by the length in metres. so a lentgth of 27.7m should read 0.05ohms.
well it's a cop out from the subsequent questions.
If the maximum value is not 0.05ohms as you repeatedly state, what in your opinion should the maximum resistance value of a main bonding connector be?
In the absence of any sensible answer to this question, I reckon I'll stick with the guidance given such as the guidance below, even if it is just a ball park / rule of thumb figure.
The resistance between any extraneous conductive part and the main earthing terminal should he 0.05 Ohms or less; all supplementary bonds are also required to have the same resistance.
http://www.tlc-direct.co.uk/Book/8.4.1.htm
ps I know that relates to 16th edition, but did anything change in terms of main earth bonding between 16-17th that would affect this? and yes, I'm aware it's also just a guide and sparks are under no obligation to follow it etc but IMO you'd need a decent logical reason why not, and this thread hasn't supplied any IMO.
Where is TLC DIRECT quoting from I bet if you look closely it's that "Extracted from The Electricians Guide Fifth Edition
by John Whitfield" I think he's been know to make mistakes
that was just one example.
I note you're still avoiding directly answering the question posed.
I'm confusticated!
Shall we restart this thread again
It all depends on the length and size of the cable a bit basic really, how can you expect anyone to come up with a max value without knowing a length and size you can't expect me to mind read, Now can you grasp "the max value of any cable/core" it's easy maths lol
- - - Updated - - -
Can't stand marmite lol
London
Main bondage
ultinator,
Dan,
TrueNAS JBOD Storage Server