Discuss Main bondage in the UK Electrical Forum area at ElectriciansForums.net
I presume that students are advised and probably instructed to read GN3 in which case that would very reasonably be viewed as a trick question.THIS IS ONE OF THE MOST FAILED QUESTIONS IN TEST AND INSPECTION EXAMS when the question has been asked state the maximum value of resistance of a main protective bonding conductor...................I REST MY CASE END OF FINISH
The figure 0.05 is just a means of confirming a connection say between a RSJ joint, simple, that's lt.
Main Bonding lust (haha...back to the thread title) needs to be sized correctly, the length Is irrelevant.
The op, he needs to ensure his test equipment is calibrated and correctly connected.
The resistance needs to relate to the length and csa.
If it doesn't he needs to identify why and remedy.
Exactly!
If the length is irrelevant and some like to say there is no upper resistance specified, you may as well use 1mm[SUP]2[/SUP].
So therefore, the resistance of the cable must have some significance.
Exactly!
If the length is irrelevant and some like to say there is no upper resistance specified, you may as well use 1mm[SUP]2[/SUP].
So therefore, the resistance of the cable must have some significance.
Archy, 1mm would be fine, when calculating touch voltage you assume little or no current in the conductor.
The min 6mm is for mechanical strength.
well thats not quite right is it ?
a minimum sized bond conductor is specified , but no upper resistance value needs to be complied with for that conductor if its the correct csa.
That's what the regs say, half the Main E C, and no resistance value specified.
But why?
That's what the regs say, half the Main E C, and no resistance value specified.
But why?
edit...
I'm sure I vaguely remember when I did my 2391 10 years ago, they said, 'If you're meter reads zero when testing bonding conductors, write down 0.01!
second thoughts what a load of tosh lol
I'm going dizzy now