Joined
May 17, 2012
Messages
178
Reaction score
17
Location
London
Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
 
THIS IS ONE OF THE MOST FAILED QUESTIONS IN TEST AND INSPECTION EXAMS when the question has been asked state the maximum value of resistance of a main protective bonding conductor...................I REST MY CASE END OF FINISH
I presume that students are advised and probably instructed to read GN3 in which case that would very reasonably be viewed as a trick question.

Furthermore, why would such a question be asked if there is no maximum resistance value?

Getting the question wrong would only result in an installation being 'safer'?
 
The figure 0.05 is just a means of confirming a connection say between a RSJ joint, simple, that's lt.

Main Bonding lust needs to be sized correctly, the length Is irrelevant.

The op, he needs to ensure his test equipment is calibrated and correctly connected.

The resistance needs to relate to the length and csa.

If it doesn't he needs to identify why and remedy.
 
The figure 0.05 is just a means of confirming a connection say between a RSJ joint, simple, that's lt.

Main Bonding lust (haha...back to the thread title) needs to be sized correctly, the length Is irrelevant.

The op, he needs to ensure his test equipment is calibrated and correctly connected.

The resistance needs to relate to the length and csa.

If it doesn't he needs to identify why and remedy.

Exactly!
If the length is irrelevant and some like to say there is no upper resistance specified, you may as well use 1mm[SUP]2[/SUP].

So therefore, the resistance of the cable must have some significance.
 
Exactly!
If the length is irrelevant and some like to say there is no upper resistance specified, you may as well use 1mm[SUP]2[/SUP].

So therefore, the resistance of the cable must have some significance.

well thats not quite right is it ?
a minimum sized bond conductor is specified , but no upper resistance value needs to be complied with for that conductor if its the correct csa.
 
Exactly!
If the length is irrelevant and some like to say there is no upper resistance specified, you may as well use 1mm[SUP]2[/SUP].

So therefore, the resistance of the cable must have some significance.

Archy, 1mm would be fine, when calculating touch voltage you assume little or no current in the conductor.

The min 6mm is for mechanical strength.
 
well thats not quite right is it ?
a minimum sized bond conductor is specified , but no upper resistance value needs to be complied with for that conductor if its the correct csa.

That's what the regs say, half the Main E C, and no resistance value specified.
But why?


edit...


I'm sure I vaguely remember when I did my 2391 10 years ago, they said, 'If you're meter reads zero when testing bonding conductors, write down 0.01!
 
Personally I think it's because water pipes gas pipes and the like can introduce additional earth paths into the electrical installation and to be comparable with the resistivity of steel pipe or the old lead and copper pipe an excepted copper cable has been estimated to achieve an excepted resistive value between these services is 10mm in most cases , mainly due to the fact that most domestic situations the bonding conductor is usually a short length of cable. Having said all that who knows .................On it goes lol
That's what the regs say, half the Main E C, and no resistance value specified.
But why?


edit...


I'm sure I vaguely remember when I did my 2391 10 years ago, they said, 'If you're meter reads zero when testing bonding conductors, write down 0.01!
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top