Joined
May 17, 2012
Messages
178
Reaction score
17
Location
London
Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
 
my point being that if you do need to achieve a 0.05ohms reading between gas and water pipes
But you don't, that is not a requirement.

All that is required is that each service is MAIN bonded to the MET with a conductor of negligible impedance (0.05Ω or less is deemed to satisfy this).

To verify this we have to measure the resistance from bonding point to MET, i.e. the conductor path.

The resistance between each service is not considered.
 
But you don't, that is not a requirement.

All that is required is that each service is MAIN bonded to the MET with a conductor of negligible impedance (0.05Ω or less is deemed to satisfy this).

To verify this we have to measure the resistance from bonding point to MET, i.e. the conductor path.

The resistance between each service is not considered.
ok, so you're saying that Voltzelectrical and KUS1 are wrong to have made or agreed with that statement?
 
Candidates are still incorrectly stated that the maximum value for the resistance of a main protective bonding conductor is 0.05 ohms.
No, that is the correct statement.

This value is applicable where access to the bonding connection is not possible
It must be accessible.

and a test is made between two extraneous conductive parts (GN3 Page 35).
Not for MAIN bonding.
Connections between e-c-ps are supplementary bonding which is not required between services and e-c-ps such as structural parts.

This value is not the maximum permitted resistance of the main protective bonding conductor.
Yes, it is.
For a part with no other connection to the MET, what else can it be?

THIS IS ONE OF THE MOST FAILED QUESTIONS IN TEST AND INSPECTION EXAMS when the question has been asked state the maximum value of resistance of a main protective bonding conductor...................I REST MY CASE END OF FINISH
What is the question?
 
What is the maximum value for resistance of a main protective bonding conductor ??? If you think it's 0.05 ohms you are wrong, if you can't understand why, well I'm sorry if I can't explain it more clearly for any of you but that's it, you'll have to just except it, perhaps someone else on this site can explain it better than me.
 
What is the maximum value for resistance of a main protective bonding conductor ??? If you think it's 0.05 ohms you are wrong,
Ok. What is the correct answer, then?
If not a specific value then the definition or means of determination.

All the regulations state is that it shall be sized appropriately with no regard to length and therefore resistance.
This is to handle fault current without damage.
Within reason, the resistance will obviously be very low.


if you can't understand why, well I'm sorry if I can't explain it more clearly for any of you but that's it, you'll have to just except it, perhaps someone else on this site can explain it better than me.
I don't think you have.
You keep mentioning the resistance between the service pipes which is not required with regard to Mian bonding.

I should be grateful if someone would.
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top