But you don't, that is not a requirement.my point being that if you do need to achieve a 0.05ohms reading between gas and water pipes
ok, so you're saying that Voltzelectrical and KUS1 are wrong to have made or agreed with that statement?But you don't, that is not a requirement.
All that is required is that each service is MAIN bonded to the MET with a conductor of negligible impedance (0.05Ω or less is deemed to satisfy this).
To verify this we have to measure the resistance from bonding point to MET, i.e. the conductor path.
The resistance between each service is not considered.
No, that is the correct statement.Candidates are still incorrectly stated that the maximum value for the resistance of a main protective bonding conductor is 0.05 ohms.
It must be accessible.This value is applicable where access to the bonding connection is not possible
Not for MAIN bonding.and a test is made between two extraneous conductive parts (GN3 Page 35).
Yes, it is.This value is not the maximum permitted resistance of the main protective bonding conductor.
What is the question?THIS IS ONE OF THE MOST FAILED QUESTIONS IN TEST AND INSPECTION EXAMS when the question has been asked state the maximum value of resistance of a main protective bonding conductor...................I REST MY CASE END OF FINISH
If you're not interested, don't read it.Can somebody enlighten me as to what this thread is about please?
Please tell me which is the correct view, then.Geoff who's rattled your cage, I have read it but there is so many contradicting opinions the whole thread has just lost its point
Ok. What is the correct answer, then?What is the maximum value for resistance of a main protective bonding conductor ??? If you think it's 0.05 ohms you are wrong,
I don't think you have.if you can't understand why, well I'm sorry if I can't explain it more clearly for any of you but that's it, you'll have to just except it, perhaps someone else on this site can explain it better than me.
What is the right answer to this question then?What is the maximum value for resistance of a main protective bonding conductor ???
It's not petty argument. Definitely not petty.I'm not interested in petty arguments like you Geoff